Controlling Upstream And Downstream Pressure
#1
Posted 30 June 2010 - 01:03 AM
Can someone kindly suggest me some methods of controlling upstream pressure as well as downstream pressure, whereby the upstream pressure should be keep at about 50 to 60bar (reject from reverse osmosis unit) and downstream pressure at 20bar maximum since the downstream equipment is sensitive to pressure.
Thanks in advance
#2
Posted 30 June 2010 - 01:17 AM
#3
Posted 30 June 2010 - 01:29 AM
#4
Posted 30 June 2010 - 05:37 AM
One of the idea which i have come out with is to have a back-pressure regulator at the reject of the RO unit and a pressure regulator just before the NF unit, thus, regulating both the pressure upstream and downstream. However, in between this section of pipes, it results in an discharge line with another backpressure regulator and compromising the feed flowrate into NF unit. Any other better suggestions or constructive feedbacks are welcome. Thanks
#5
Posted 30 June 2010 - 06:40 AM
#6
Posted 30 June 2010 - 11:38 AM
If nothing else, you can post a sketch here (include all the existing regulation loops) and I'm sure we can resolve the problem.
Good luck,
#7
Posted 01 July 2010 - 10:38 AM
#8
Posted 08 July 2010 - 03:27 AM
Dear,Hi,
Can someone kindly suggest me some methods of controlling upstream pressure as well as downstream pressure, whereby the upstream pressure should be keep at about 50 to 60bar (reject from reverse osmosis unit) and downstream pressure at 20bar maximum since the downstream equipment is sensitive to pressure.
Thanks in advance
As specified by that the limit for downstream pressure of 20 bar can be maintained by a PIC taking pressure signal from downstream PT. Now in case of upstream pressure could you tell us what develops this much of the pressure of 50-60 bar? You problem is quite similar to PRDS where the downstream steam headers' pressures are maintained on PIC and upstream excess pressure is vented through a silencer. So in your case the if the upstream pressure goes higher as the downstream is maintained at 20 bar then you need other option to relieve it through an upstream PT signal. Again you have issue when an upstream pressure falls down the downstream PIC will open wide to maintain 20 bar in the downstream. It's bit complicated. Provide us a sketch and little description of the system so that we can comment.
Similar Topics
![]() Negative Pressure Discharge / Negative At High PointStarted by Guest_felderosfelder101021_* , Yesterday, 07:10 AM |
|
![]() |
||
![]() Rupture Disc Failure Well Below Max PressureStarted by Guest_vaibhav02_* , 02 Jul 2025 |
|
![]() |
||
![]() Distillation Column Top PressureStarted by Guest_halkeshhulk_* , 27 Jun 2025 |
|
![]() |
||
![]() Recommended Installation Location For "pressure High" InterlocStarted by Guest_omupei_* , 20 Jun 2025 |
|
![]() |
||
Parallel Control Valves Downstream Relief ScenarioStarted by Guest_pklavinsJ_* , 18 Jun 2025 |
|
![]() |