At this moment I am reviewing a Control Narrative for Duty Control in Stripper Column Reboiler.(MEA+H2S). This narrative indicates that the steam control valve is located in the steam line (steam inlet). However in another control narratives reviewed before, I could observe that the steam control valve is located in the condensate line (steam condensate). I was looking for the best practices for such design, it means where the steam control valve should be located, but I could not find anything related.
In my personal opinion if the control valve is installed in the inlet steam then a delta P will be generated and the temperature of the steam to the reboiler will be affected. But I think that the Process Engineer who designs this system has to considerate such effect and to use the latent heat (hfg) and avoid an undesirable thermodynamic state in the steam to reboiler once leaves the control valve.
I would appreciate your help with this topic.
First of all, is a pleasure being in this forum.
At this moment I am reviewing a Control Narrative for Duty Control in Stripper Column Reboiler.(MEA+H2S). This narrative indicates that the steam control valve is located in the steam line (steam inlet). However in another control narratives reviewed before, I could observe that the steam control valve is located in the condensate line (steam condensate). I was looking for the best practices for such design, it means where the steam control valve should be located, but I could not find anything related.
In my personal opinion if the control valve is installed in the inlet steam then a delta P will be generated and the temperature of the steam to the reboiler will be affected. But I think that the Process Engineer who designs this system has to considerate such effect and to use the latent heat (hfg) and avoid an undesirable thermodynamic state in the steam to reboiler once leaves the control valve.
I would appreciate your help with this topic.
#2
Posted 07 July 2010 - 12:51 AM
The basic difference in having (1) steam, or (2) condensate flow control in reboilers is:
1. By having control valve in the steam supply line, the condensation pressure inside the reboiler channel head (and thus the steam condensing temperature) is varied. If you look at the basic heat transfer equation Q = U*A*LMTD, doing this way changes the effective temperature difference in the reboiler and therefore the heat transfer rate as well.
2. By having control valve in the condensate outlet line, the number of tubes in reboiler submerged in condensate is varied by manipulation of the condensate outflow. In such way, the net area available for heat transfer is changed as well (Q = U*A*LMTD).
Both schemes have their advantages and disadvantages, and one of the best places to see pro's and con's of each scheme is Walter Driedger's article attached below.
1. By having control valve in the steam supply line, the condensation pressure inside the reboiler channel head (and thus the steam condensing temperature) is varied. If you look at the basic heat transfer equation Q = U*A*LMTD, doing this way changes the effective temperature difference in the reboiler and therefore the heat transfer rate as well.
2. By having control valve in the condensate outlet line, the number of tubes in reboiler submerged in condensate is varied by manipulation of the condensate outflow. In such way, the net area available for heat transfer is changed as well (Q = U*A*LMTD).
Both schemes have their advantages and disadvantages, and one of the best places to see pro's and con's of each scheme is Walter Driedger's article attached below.
Attached Files
#3
Posted 07 July 2010 - 08:24 AM
Thank a lot Zauberberg!! Excellent information and article.
Regards!
Regards!
#4
Posted 08 July 2010 - 03:50 AM
Dear Zauberberg,The basic difference in having (1) steam, or (2) condensate flow control in reboilers is:
2. By having control valve in the condensate outlet line, the number of tubes in reboiler submerged in condensate is varied by manipulation of the condensate outflow. In such way, the net area available for heat transfer is changed as well (Q = U*A*LMTD).
I have a confusion here, could you tell me how I could vary the heat transfer area in case of a reboiler when the condensate is routed to a condensate pot and it's level is controlled. Now the reboiler elevation and the condensate pot elevation are different i.e. cond pot is at relatively lower elevation (generally on the grade). In this case I am not sure about the submergence of tube in condensate in reboiler.
#5
Posted 08 July 2010 - 12:05 PM
Hello Padmakar
Look more closely at the P&ID: if level in the reboiler cannot be controlled (either directly or through the pot) then there must be a control valve in the steam supply line. See attached.
Best regards,
Look more closely at the P&ID: if level in the reboiler cannot be controlled (either directly or through the pot) then there must be a control valve in the steam supply line. See attached.
Best regards,
Attached Files
Similar Topics
Levels For Kettle Type ReboilerStarted by Guest_RajD_* , 04 Apr 2025 |
|
![]() |
||
Phe As ReboilerStarted by Guest_Chemeng40_* , 20 Feb 2025 |
|
![]() |
||
![]() How To Replace Existing Reboiler With A Thermosyphon Reboiler In HysysStarted by Guest_tomr91_* , 04 Feb 2025 |
|
![]() |
||
Surge Analysis-Control LogicsStarted by Guest_stu_* , 30 Dec 2024 |
|
![]() |
||
![]() Pump Dischrge Control Valve SizingStarted by Guest_Lyne_* , 04 Jun 2024 |
|
![]() |