#1 Rahimzadeh

Rahimzadeh

    Gold Member

  • Members
  • 282 posts

Posted 12 November 2010 - 02:06 AM

dEAR FRIEND:
Is possible anybody tell me about gas pressure in burner tips.
Best regards

#2 Zauberberg

Zauberberg

    Gold Member

  • ChE Plus Subscriber
  • 2,728 posts

Posted 12 November 2010 - 03:30 AM

The pressure at the burner tip varies, and it is changed either by the panel operators or by the primary control loop (e.g. process stream outlet temperature cascaded to the fuel gas flow/pressure controller). Each type of burner has its own Heat release vs. Pressure curve, also providing you with the minimum/maximum fuel gas pressure values.

#3 Flame

Flame

    Junior Member

  • ChE Plus Subscriber
  • 28 posts

Posted 12 November 2010 - 10:05 AM

Typical values seen are in the range 1.5 - 2.0 kg/cm2g @ max load. However, exact value needs to be confirmed after performing fuel gas line hydraulics and then specified to the burner vendor for engineering at his end.

#4 Rahimzadeh

Rahimzadeh

    Gold Member

  • Members
  • 282 posts

Posted 13 November 2010 - 12:01 AM

Dears:
Thanks for your nice response.
I want to know the gas pressure in burner and pilot exact before lighting up?
thank you

#5 Zauberberg

Zauberberg

    Gold Member

  • ChE Plus Subscriber
  • 2,728 posts

Posted 13 November 2010 - 05:16 AM

Rahimzadeh,

This information should be readily available in the Plant Operating Manual, and within the Burner Datasheet as well.

Thess values vary from plant to plant, and if you are asking for any particular system - such data have to be provided within supplied equipment information. There is no such thing as "universal pilot gas pressure", or "lightning burner tip pressure".

#6 Rahimzadeh

Rahimzadeh

    Gold Member

  • Members
  • 282 posts

Posted 14 November 2010 - 12:31 AM

Dear SIR:
I BELEIVE THERE IS NO UNIVERSAL STANDARD FOR THIS PARAMETER .
BUT THERE IS A NORM THAT ACCEPTED AS NORM BY BOILER OR BURNER MANUFACTURER.

WE ARE LOOKING FOR SUCH NORM
FOR YOUR MORE INFORMATION OUR BOILER SPECIFICATION IS AS FOLLOW:
1-NORMAL STEAM DRUM PRESSURE:11.6 BARG (SATURATED)
2-MAX RATE:55 TON/HR
3-NORMAL RATE :45 TON/HR
4-FUEL GAS COMPOSITION : A-METHANE 82% AND B- ETHANE 14%
BEST FOR YOU

#7 Zauberberg

Zauberberg

    Gold Member

  • ChE Plus Subscriber
  • 2,728 posts

Posted 14 November 2010 - 08:30 AM

I had a look into the online IPS standards, and it says the following:

The pilot gas, where practicable, shall be taken from a sweet gas supply, independent of the main burner gas, or from a separate off-take on the fuel gas main, with its own block valve and spade-off position. Unless otherwise approved by Company, the pilot gas pressure shall be controlled at 35 kPa (0.35 bar) and the pressure regulating valve shall be the self-operating type.


For fuel gas systems and boilers, read more at:

http://igs.nigc.ir/ips/pr/e-pr-340.pdf
http://igs.nigc.ir/ips/pr/e-pr-800.pdf

Good luck,