Psv Vent Height
#1
Posted 16 July 2011 - 02:47 AM
I'm Dealing with a Gas Pressure Reduction Station Project for a Power Plant Project(GTGs).
There are some PSV's with Discharge to Safe location route.
My question is about the vent stack height result of API-521 standard.
In one Case our data are as bellows:
Discharge of PSV to Atm.(as per P&ID) : 4"
Relief load = 11600 Sm3/hr ~ 7871kg/hr
Ro(Methane at 25C and 0barg)=0.68(Disch. To Atm.)
V(at discharge of stack) = (7871*2/3600)/0.68*(pi/4*(4*0.0254)^2)=793.6 m/s >444 (m/s)[Sound velocity in methane at 15C and 0barg]-------> we have Chocke flow
Re=ro*V*d/mo = 0.68*444*0.1016/0.000011= 2788463 > 15400*(roj/ro∞)=8845
so we have jet domminant flow
There are 3 points in API-521-2008:
1- as Per equation 23 of API
y= the height at which typical hydrocarbon relief streams are diluted to their lower flammable limit=12m
2-As per Figure-4 with considering of 10m/s for air velocity
X=(u∞/ uj)=10/444=0.0225
Y=85=y/0.1016*Sqrt(roj/ro∞) y=85*0.1016*0.758=6.55 m and 13 m for still air
3- bellow item in API:
7.3.4 Vent stacks
7.3.4.1 Sizing
Where the atmospheric vent handles combustible vapours, the outlet from the vent should be elevated
approximately 3 m (10 ft) above any adjacent equipment, building, chimney or other structure
Now I'm Confused, Which height Should be considered for vent stack.
Do I need a precise Calculation of dispersion, for example a PHAST Analysys?
Is 13 m height reasonable ?
I couldn't find a GPR Station with such a vent height for their stack.
Thanks alot
#2
Posted 16 July 2011 - 05:09 AM
Dear friends
I'm Dealing with a Gas Pressure Reduction Station Project for a Power Plant Project(GTGs).
There are some PSV's with Discharge to Safe location route.
My question is about the vent stack height result of API-521 standard.
In one Case our data are as bellows:
Discharge of PSV to Atm.(as per P&ID) : 4"
Relief load = 11600 Sm3/hr ~ 7871kg/hr
Ro(Methane at 25C and 0barg)=0.68(Disch. To Atm.)
V(at discharge of stack) = (7871*2/3600)/0.68*(pi/4*(4*0.0254)^2)=793.6 m/s >444 (m/s)[Sound velocity in methane at 15C and 0barg]-------> we have Chocke flow
Re=ro*V*d/mo = 0.68*444*0.1016/0.000011= 2788463 > 15400*(roj/ro∞)=8845
so we have jet domminant flow
There are 3 points in API-521-2008:
1- as Per equation 23 of API
y= the height at which typical hydrocarbon relief streams are diluted to their lower flammable limit=12m
2-As per Figure-4 with considering of 10m/s for air velocity
X=(u∞/ uj)=10/444=0.0225
Y=85=y/0.1016*Sqrt(roj/ro∞) y=85*0.1016*0.758=6.55 m and 13 m for still air
3- bellow item in API:
7.3.4 Vent stacks
7.3.4.1 Sizing
Where the atmospheric vent handles combustible vapours, the outlet from the vent should be elevated
approximately 3 m (10 ft) above any adjacent equipment, building, chimney or other structure
Now I'm Confused, Which height Should be considered for vent stack.
Do I need a precise Calculation of dispersion, for example a PHAST Analysys?
Is 13 m height reasonable ?
I couldn't find a GPR Station with such a vent height for their stack.
Thanks alot
The vent stack is form one PSV or from vent header (from multiple PSVs)?
I think 13 m height is reasonable, based on dispersion and radiation criteria on API 521.
#3
Posted 16 July 2011 - 06:10 AM
Dear friends
I'm Dealing with a Gas Pressure Reduction Station Project for a Power Plant Project(GTGs).
There are some PSV's with Discharge to Safe location route.
My question is about the vent stack height result of API-521 standard.
In one Case our data are as bellows:
Discharge of PSV to Atm.(as per P&ID) : 4"
Relief load = 11600 Sm3/hr ~ 7871kg/hr
Ro(Methane at 25C and 0barg)=0.68(Disch. To Atm.)
V(at discharge of stack) = (7871*2/3600)/0.68*(pi/4*(4*0.0254)^2)=793.6 m/s >444 (m/s)[Sound velocity in methane at 15C and 0barg]-------> we have Chocke flow
Re=ro*V*d/mo = 0.68*444*0.1016/0.000011= 2788463 > 15400*(roj/ro∞)=8845
so we have jet domminant flow
There are 3 points in API-521-2008:
1- as Per equation 23 of API
y= the height at which typical hydrocarbon relief streams are diluted to their lower flammable limit=12m
2-As per Figure-4 with considering of 10m/s for air velocity
X=(u∞/ uj)=10/444=0.0225
Y=85=y/0.1016*Sqrt(roj/ro∞) y=85*0.1016*0.758=6.55 m and 13 m for still air
3- bellow item in API:
7.3.4 Vent stacks
7.3.4.1 Sizing
Where the atmospheric vent handles combustible vapours, the outlet from the vent should be elevated
approximately 3 m (10 ft) above any adjacent equipment, building, chimney or other structure
Now I'm Confused, Which height Should be considered for vent stack.
Do I need a precise Calculation of dispersion, for example a PHAST Analysys?
Is 13 m height reasonable ?
I couldn't find a GPR Station with such a vent height for their stack.
Thanks alot
The vent stack is form one PSV or from vent header (from multiple PSVs)?
I think 13 m height is reasonable, based on dispersion and radiation criteria on API 521.
Thanks for your reply.
It's from vent header(Multiple PSV)
I've seen lots of GPR station around different cities in my country, but I havn't seen such a high stack there.
#4
Posted 16 July 2011 - 07:15 AM
You already re-calculate the height based on the criteria of radiation and dispersion?
#5
Posted 01 August 2011 - 05:29 AM
Sorry for delay.
No. I've never done disperssion calculation.
Could you please reccomend me some useful references(Book-paper or softwares) for this calculation.
Thanx.
Similar Topics
Convert No. Of Trays Into Packing HeightStarted by Guest_T_bag_* , 20 May 2026 |
|
|
||
Minimum Distance Between Blowdown Valve And Cold Vent Outlet In A HighStarted by Guest_AMINEBELAL_* , 15 May 2026 |
|
|
||
Gas Blanketing Vent Size For Atmospheric Storage TankStarted by Guest_Fergie_* , 13 Apr 2026 |
|
|
||
Drain And Vent Destination LpgStarted by Guest_Priolo_* , 14 Feb 2026 |
|
|
||
Atmospheric Tank Vent SizingStarted by Guest_kmic_* , 30 Sep 2025 |
|
|

FB