High Sound & Vibration From Screw Pump (Fuel Oil Service)
#1
Guest_Nish_*
Posted 31 August 2011 - 12:38 AM
We have proposed a screw pump for 680Cst HFO with a capacity 1500m3/hr along with a heating system. The client have installed the pumps but not the heating system and started pumping 380Cst product. But they are experiancing a very high sound and vibration. I have checked the available and required NPSH ie NPSH required is 5.4mWC and the pressure available at the suction nozzle of the pump is 65KPaa (6.62mWC).
During the test run we have observed a suction pressure of 0.4barg at suction. To my understanding the cause points to cavitation due to lack of heating system.
Can we mitigate this problem with out installing a heating system. I would appreciate if you share if you have a different openion or solution.
Br,
Nish
#2
Posted 31 August 2011 - 09:14 AM
-Assuming HFO sg = 1.0, NPSHr=5.4 m CL in pump data sheet; suction pressure = 1.41 bara during test (14.4 m CL). What was operating temperature of (non heated) fuel oil during test? Vapor pressure of "dry" fuel oil is usually quite low (to ensure flash point>60 oC), but vapor pressure of any water content is additive to it, since the two liquids are not miscible. Moreover HFO temperature should be at least 90 oC to suspect cavitation from water vapor (vap press = 0.7 Bara) under test conditions, and this 90 oC is probably higher than operating temperature. Anyway check both water and HFO vapor pressures at actual operating temperature.
-Can you feed the screw pump with another liquid (water at ambient temperature?) to see whether it runs smoothly? You can exclude pump mechanical problem in this way.
-At the end I would repeat the test using fuel oil with more instruments (at any case additional suction manometer for verification of 0.4 Barg) in the presence of a representative of pump supplier.
-HFO heating to a higher temperature (i.e. reducing suction frictional ΔP) is not certain to solve the problem, according to my understanding.
Edited by kkala, 01 September 2011 - 01:59 AM.
#3
Posted 01 September 2011 - 10:20 AM
380cst is the viscosity at 50C.
At 20C: 4,650cst (approx, based on CIMAC data for a 390cst fuel)
At 30C: 1800cst
At 40C: 790cst....
Heating is important.
Especially for the intended 680cst....
AT 20C: 10,200cst
At 30C: 3,600cst
at 40C: 1500cst
It isn't just cavitation due to the suction problems, but if you do get the discharge line primed the headloss may cause the pressure relief valve to trip so you will be recirculating fuel outlet to inlet.
#4
Guest_Ikka_*
Posted 03 September 2011 - 01:09 AM
Here is more details about the fluid
Density @ 50C = 930kg/m3
Vapr. Pr = 1.3KPaa
The temperaturing during the pumping was ambient temp (arnd 35degC). Our proposed operating temperature is 50degC but they can't maintain that temp as they do not have the heating system at present. I can not feed feed these lines with anyother fluid at this moment as this is a dedicated HFO system.
At the same time I proposed them to do a test by flushing and cleaning the suction line back to one tank and then take suction from a tank with full level HFO. This is see whether ΔP is prominent. Also asked them to open the suction valve and tank valve to prime the pump before start. I'm waiting for its result.
BTW I suspect the heating because the night temp her sometime go to 15-20degC which enhance coagulating the HFO on the walls and these agglomerates when flow to the pump will create more problem. Need you guys enlighten me on this
I have attached the hydraulic calculation summary for more info.
Attached Files
#5
Guest_Ikka_*
Posted 03 September 2011 - 01:29 AM
Thanks for sharing the viwscosity details. The pump is intented to pump 680Cst at 50deg C where as during our trial run we used 360Cst at ambient temp of about 35degC.
When you say suction problem, did you mean the piping arrangement? For info I suction piping problem because an elbow is located very near to the pump suction nozzle. Piping arrangement is bit complicated too.
Regarding PRV trip, the client told me that they were getting some reasonable flow in the dischage but later we have observed that there is a leakage in the PSV. Are you pointing to chattering from PSV? I would appreciate if you explain with more details.
I'm really happy to see good comments, I think I have to link with this website more often.
Thanks
Ikka
#6
Posted 03 September 2011 - 07:55 AM
-It is noted that heavy fuel oils stored here (s.g. =0.95-0.98) would require continuous heating to (say) 55 oC; handling temperature of 35 oC (lower in the night) seems too low. But suction pressure of 0.4 Barg (as measured) is in excess of what you need. So measurement of suction and discharge pressure during test run has also to be continuous and reliable.
-Mentioned cleaning and priming of suction line are judged to be on the right direction.
-I think fuel oil gums (rather from polymerization / oxidation) are formed in long time; in your case fuel oil can be locally viscous (or even agglomerated?) due to moderate cold, and this could remain during day; but a screw pump is generally tolerant to it; and suction line is not plugged, since it has enough suction pressure at rated flow. So ambient 15-20 oC at night may not have a significant result, on the condition that suction pressure remains at 0.4 barg during test run.
-Probably it is good to call an engineer of the pump supplier to solve the problem, if it continues. Will the supplier be present during the pump commissioning? This is normal practice here, especially for pumps of such size.
#7
Guest_Ikka_*
Posted 04 September 2011 - 02:38 AM
I think I'm clear on this issue let me have this test run and I will post the result here.
- I didn't thought about the undissolved water and its vaporisation. I will have to study on this more
- my only concern remaining is whether the chattering of PSVs creating the sound and vibration. Because we have five pumps in parellel and each discharge line has a PSV upstream of the check valve.
We should close this thread if chattering is not an issue. I love to have a healthy thread which can be a good reference for others.
Br,
Ikka
#8
Posted 04 September 2011 - 05:07 AM
Concerning event of PSV chattering, I suppose you could detect whether noise comes from pump or PSV, if you approach the pump discharge closely.
I remember plant operators able to detect cavitation from the characteristic noise of the specific pump, in the common case when cavitation produces noise. So probably an operator could diagnose PSV chattering from the noise.
Water mixed with fuel oil is not expected to cause cavitation at 35 oC operating pressure.
Edited by kkala, 04 September 2011 - 05:10 AM.
#9
Posted 05 September 2011 - 07:18 AM
While cavitation may not be a problem, flashing off of volatiles may be.
Since the client didn't include the heaters, did they also neglect insulation? What ever heat the fuel has ought to be preserved as best as possible though, to be fair, insulation is often more about protecting operators from hot pipes than it is to conserving heat or energy.
I know of cases with bitumen installations where local cols spots caused complete blockages. In instances where there was not proper protection the pump simply kept running and ballooned the flow meter till the bolts sheared.
If this isn't continuous flow, do they flush the lines with diesel or reverse flow the pump to empty the pipes back into storage?
Starting cold with a flooded pipe can be an issue both for suction and discharge. I have come across some installations where they just couldn't get any reasonable flow from a cold start (and in one installation they used flexible couplings which simply collapsed).
Now, if the discharge is partially blocked, the pressure relief bypass will cut in. But if the suction is starved? Kkala?
PS.You quoted the density as 930kg/m3 at 50C which is 950.4kg/m3 at 15C which fits with expectations and the range of values Kkala mentioned.
#10
Posted 05 September 2011 - 03:49 PM
Volatiles could cause even cavitation by increasing fuel oil vapor pressure, but normally these are controlled indirectly to keep fuel oil flash point below 66 oC.
Edited by kkala, 05 September 2011 - 04:04 PM.
Similar Topics
Centrifugal Pump In Recycle Mode: Constant Power Consumption But FluctStarted by Guest_Kakka_* , 23 Jan 2025 |
|
![]() |
||
Need Help Understanding Increased Power Consumption In Injection PumpStarted by Guest_Kakka_* , 21 Feb 2025 |
|
![]() |
||
Improving Safety By Re-Routing Priming Vent Line In Centrifugal Pump HStarted by Guest_Srinivas Agastheeswaran_* , 31 Jan 2025 |
|
![]() |
||
Screw Compressor Suction Pressure DeterminationStarted by Guest_Deicide Dunkelheit_* , 22 Jan 2025 |
|
![]() |
||
![]() High Stack Temperature In Ccr HeatersStarted by Guest_viba0124_* , 30 Nov 2024 |
|
![]() |