Shall We Have Knock-Out Drum In Lpg Flare Line
#1
Posted 06 October 2011 - 01:30 AM
We have flare line connected with the Cold flare & hot flare. But we dont have the Knock-out drum in the flare line.
But i heard that knockout drum is used in flare line just before the Flare chimney.
What is the purpose of knock-out drum...?
What is the standard, which mentioned the use of knockout drum in flare line...?
As per your views, we will install the knockout drum in the flare line.
#2
Posted 06 October 2011 - 01:59 AM
Purpose of knock out drum in flare line is to separate liquid droplets larger than 300-600 micro meter in diameter to avoid entrance of such droplets into flare stack/tip.
In LPG flare line the knock out drum is usually being considered.
For more detail please refer to API STD 521.
Fallah
Edited by fallah, 06 October 2011 - 02:02 AM.
#3
Posted 06 October 2011 - 02:10 AM
But LPG will evaporate in atm pressure. So liq. LPG comes out in flare tip as LPG Gas.
Am i right...? then what is the effect of liquid droplets larger than 300-600 micro meter in flare line. Anyway it will come out of flare tip in gas state.
Do you know, any plant using knockout drum for LPG flaring application....?
#4
Posted 06 October 2011 - 03:09 AM
You are generally right...... the LPG will evaporate in atmospheric pressure (of course in temperature not so low)..... but liquid LPG from relif point up to stack hasn't enough time to absorb needed latent heat to become vapor completely. Even in most cases it is needed to install electrical (or steam) heater in knock our drum to assist LPG evaporation in order to avoid LPG liquid carry over into the stack!
Entrance of droplets larger than 300-600 micro meter into the flare tip can result in incomplete combustion along with excessive smoking that will lead to burning rain and flame out.
Yes, in one plant i was involved in its design knock out drum has been considered for LPG flaring.
Fallah
Edited by fallah, 06 October 2011 - 03:10 AM.
#5
Posted 06 October 2011 - 02:20 PM
LPG can contain quite small amounts of pentane (b.p. of n-C5 = 36 oC), or even traces of heavier hydrocarbons. Probably you have detected condensates in hot or (especially) in cold flare line. All these indicate a good reason to install knock out drum upstream of flare. But have you observed condensate or do you estimate liquid formation under certain (not normal) conditions?
Edited by kkala, 06 October 2011 - 02:24 PM.
#6
Posted 07 October 2011 - 05:26 AM
--> Mr Fallah --> My observation is LPG burns in black, incomplete combustion. Also Liquid falls near the flare stack also occurs. Due to this incomplete combustion, CO2 emission will also be more, i suppose.
Hi Kkala, i have seen water condensate (even ice formation) on the flare line. The reason is the LPG expansion. am i right? does this have any bad effect (or) its normal...?
Knockout drum will be installed just before the flare stack. So how it will prevent the condensate formation...?
Can you give me any link or file, showing the process of knockout drum..?
#7
Posted 07 October 2011 - 07:56 AM
http://www.geekinter...ckout-drum.html
http://kolmetz.com/p...re%20Rev1.1.pdf
http://www.gasflare..../Flare_Type.pdf.
A knock out drum collects the liquid droplets already formed, it does not prevent droplet formation.
You are right, as LPG expands (from e.g. a PSV) into flare header, fall of temperature can create liquid droplets or even ice. This indicates necessity of knock out drum to collect these droplets.
Since LPG specifications call for almost zero water content (http://www.iocl.com/...cifications.pdf), conclusion is that condensate is not composed of water but of liquid hydrocarbons in most of the cases. Water is carefully monitored in LPG http://www.kinetic.c...%20Analysis.pdf.
All data found out seem to support knock out drum installation.
Edited by kkala, 07 October 2011 - 08:00 AM.
#8
Posted 07 October 2011 - 08:45 AM
In our plant, distance from flare stack to process area is 30 mtr. If we want to drain filter, we open the filter's blowdown valve, LPG flow to the flare. I was talking about the water droplets & ice formation in the outer area of the pipe. Are you also talking the same...?
Also the knockout drum will be at 28 mtr from filter. Will it help...?
In knockout drum design, they say that Vap.LPG will go to flare. what abt Liq. LPG?
Slowly, the liq.LPG also vaporises and go to flare.
#9
Posted 08 October 2011 - 02:47 AM
--> Mr Fallah --> My observation is LPG burns in black, incomplete combustion. Also Liquid falls near the flare stack also occurs. Due to this incomplete combustion, CO2 emission will also be more, i suppose.
Nezamani,
Considering your above mentioned observations:
Why do you hesitate regarding the installation of a knock out drum before LPG flare stack?
Fallah
#10
Posted 08 October 2011 - 03:06 AM
I shall have submit a proofs like any Standards (OISD,ASME,etc), code(API,etc) for making my seniors accept this proposal.
That's why i am asking any references.
I have gone thru API 521, it shows that liq. particles of more than 600 mic. will be in the bottom of the KO Drum. This will be pumped to the process line. This is like we can recover some LPG being flared. Am i right...?
#11
Posted 08 October 2011 - 03:52 AM
-- Unfortunately I worked in Operations (concerning a fertilizer plant) long ago (1976-81), mentioned LPG vaporizer with flare was in an engineering design of another fertilizer plant (1985, no filter). The question is whether you have detected condensates / liquid droplets inside pipe. Resulting low temperatures inside the pipe combined with air humidity can create ice outside during discharge. This is usual in branch lines to flare line, in your case it occurs also in main flare header. Valves in potentially 'frozen' lines should be heat traced, so that frost will not block them.
2. Also the knockout drum will be at 28 mtr from filter. Will it help...?
-- It should be quite close to flare stack, placed at 28 m (of 30 m total length) seems OK.
3. In knockout drum design, they say that Vap.LPG will go to flare. what abt Liq. LPG? Slowly, the liq.LPG also vaporises and go to flare.
-- You can pump condensates out (as you already said). Operation is critical in the sense that drum should never be full enough to allow liquid entrained to flare. This can mean standby pump, fed from critical power supply.
Alternatively drum content can be heated (http://www.eng-tips....d=146638&page=7), apparently under similar safety provisions.
Edited by kkala, 08 October 2011 - 03:54 AM.
#12
Posted 08 October 2011 - 03:56 AM
in addition to what already been contributed, a good reason to have a KO drum is preventing two phase flow. how unlikely it might sound but in case you do have two phase flow and your lines are not design for that it will damage the lines. I've seen an entire flare header jump over it support, luckily it did not harm people or major equipment.
cheers,
sm
#13
Posted 08 October 2011 - 04:22 AM
If you have any doc or links, kindly share with me.
Hi KKALA, How can we see the condensate formation in inner surface of the LPG flare pipe ?
Also the reason for outer area ice formation is, any process equipment(Pump, filter, etc..) are in the pr of more than 20 Kg/cm2. When we open the blowdown valve, LPG flows from 20 to the flare tip, which is at atm. pr. This pr. drop make the Liq.LPG to observe the latent heat and becomes Vap.LPG. So water droplets or ice formation occurs in the outer surface of the pipe. Do you agree with me...?
#14
Posted 08 October 2011 - 12:11 PM
I assume a (low point) drain pot (if any) can collect condensates. If there is a water seal drum, heavier hydrocarbons could be traced in its water. There may be other methods of detection. Frozen or cold header up to flare during a big discharge can be also a strong indication for inside liquid.
Edited by kkala, 08 October 2011 - 12:15 PM.
#15
Posted 09 October 2011 - 08:37 PM
yes, this was an LPG flare, but I dont have much doc to share. the design is very simple, just to have capacity to hold any liquids for say 5-15 min (depending on the process). these likley be from vessel liquid overfilling
as for seal drum in LPG service, you better use glycol fluid rather than water. the latter freezes and can plug the flare line especially if submerged in it.
regards,
sm
#16
Posted 09 October 2011 - 09:56 PM
Kindly add or correct the below statements,
Purpose of the KO drum is
1) To seperate the LPG liq.particle size of more than 300 microns.
2) To prevent the liq. spray from hot or cold flare
3) To have a complete combustion of the LPG vapors and prevent excessive smoking, burning rain and flame out.
For LPG KO drum applications, we dont need any pump to take out the liq. in bottom of the KODrum. As this Liq. slowly vaporise and exits in the flare. Am i right..?
Is KO drum is useful for cold vent also...?
So we will install the knock out drum just before the hot flare stack.
#17
Posted 10 October 2011 - 04:03 AM
For LPG KO drum applications, we dont need any pump to take out the liq. in bottom of the KODrum. As this Liq. slowly vaporise and exits in the flare. Am i right..?
Nesamani,
Care should be taken to apply the above conclusion for all cases!
Actually, need to a pump to take out the LPG from relevant KO drum depends on size of drum, maximum inventory once to be released to drum, frequency of receiving such inventories,...., and as far as i know in many applications even with having submerged electrical heater to assist LPG vaporization pumps have been installed to take out the LPG from the drum.
Fallah
#18
Posted 10 October 2011 - 09:36 AM
We dont want the liq.LPG to be pumped back. Let it take its time to become vapor and exits.
In normal maintenance, we vent max of 1.5 MT of LPG at a time.
Does KO drum has any dis-advantages...?
#19
Posted 17 October 2011 - 11:39 AM
- each vessel or container be it a KOD(knock out Drum)
- has a limited capacity and without any pump-out arrangement.
- It is bound to fill(eventually) topped up with liquid(slightly depends on ambient temperatures)
- As such Nobody can assure No liquid fire rain from flare tip if excessive slug finds it way up to flare-tip.
#20
Posted 18 October 2011 - 03:32 AM
2. Having liquid overfilling and carried over to flare stack is even more dangerous than having a mixture of vapor and liquid.
3. Have you done any flash calculation to determine the amount of liquid?
4. API RP 521 recommends 20-30 minutes hold-up volume.
#21
Posted 18 October 2011 - 04:49 AM
- One has to be very clear about the conceptual safety in design
- to avoid "pitfalls" and "disasters,catastrophes" from being repeated time and again.
Hope this helps/ everything will be duly taken care off.
#22
Posted 18 October 2011 - 06:55 PM
2. Where to dispose the hold-up volume?
3. 3 feasible options
1. Natural evaporation - this will take sometime. Waste of valuable product
2. Install steam coil - faster than 1st option. Add cost but waste of valuable product
3. Pump-out - recovery of valuable product. This add cost but with economic return
4. Whatever it is - "Safety First"
Edited by S.AHMAD, 18 October 2011 - 07:00 PM.
#23
Posted 20 October 2011 - 05:13 AM
However just to further clarify
- the normally existing KOD's (physical point) pressure conditions are most usually a very low (much lower than) other upstream system segments and components
- to permit UN-obstructed maximum De-pressurization possible within minimum possible time
- to ensure all upstream system components staying safe and healthy
- with simultaneously ensuring that this Knock out vessel/drum (if available) is never subjected to very high pressures.
All this necessitates a pump-out system in-place
- to remove any or all condensed liquids of any kind
- be it the LPG,Naphtha like H-C's or any other material traveling to the sky-flare
- for disposal in emergency or near emergency conditions of plant's upstream.
#24
Posted 21 October 2011 - 07:23 AM
Steam coil is another option instead of pumps. Does it have wide application in flare knock out drums? Advice on it would be welcomed.
Suppose that the knock out drum is being filled with droplets of liquid. As far as I see, it is not easy to predict total volume of liquid to be collected, how can we be sure that this will not be repeated before emptying the drum? So we had better not let liquid in the drum for long time.
Drum capacity covers the 20 min time for the operator to find the reason of liquid entrainment and eliminate it, but then it has been (almost) full. It can remain almost full for long (natural evaporation is assumed slow), in case that collected liquid is not forced to go out.
Similar Topics
Ammonia Line Vapor GenerationStarted by Guest_simadri_* , 07 Apr 2025 |
|
![]() |
||
![]() Flow Through Normally No Flow LineStarted by Guest_iippure_* , 08 Apr 2025 |
|
![]() |
||
Inlet Line Not Free DrainingStarted by Guest_Asifdcet_* , 07 Apr 2025 |
|
![]() |
||
![]() Flare Header Reverse FlowStarted by Guest_Ahmadhamzahperta_* , 04 Apr 2025 |
|
![]() |
||
Improving Safety By Re-Routing Priming Vent Line In Centrifugal Pump HStarted by Guest_Srinivas Agastheeswaran_* , 31 Jan 2025 |
|
![]() |