hello785230,
Reading your edited entry,
You need product to be cooled to 95°F. Your approach temperature for refrigerant exchanger is 5°F, which means your refrigerant temperature can be up to a maximum temperature of 95-5 = 90°F
Since your refrigerant is pure (propylene), the refrigerant temperature will be constant for that particular level. The refrigerant will evaporate from liquid to vapour phase in the shell side of an exchanger (at 90°F) and thereby cool the product to a temperature of up to 95°F. The vapour generated in the evaporator will then go to the suction of the refrigeration compressor.
The above is considering only the particular product stream that you mentioned. In practise, when there are several exchangers that need refrigerant supply (as is normal in an ethylene production plant), There will be up to five different levels of propylene refrigerant and upto four levels of ethylene refrigerant (assuming pure refrigerants). The levels are determined based on optimising the total power required for the refrigeration. Pinch Analysis can be a tool used for this purpose. Since I am not aware of the scope of your project, my response can be limiting.
Edited by pavanayi, 29 November 2011 - 01:37 PM.