I was involved in one of the separation of gas, water and condensate project. I went through the separator package and found that the all separator looks alike. Please see attached P & ID.
I have founded following error but no one agree with me.
(1)Mist Eliminator should be installed on other chamber (bucket side) so all gas can pass through the mist eliminator.
(2) We don’t need bucket if we are providing Boot OR don’t need boot if providing bucket.
(3) LT-904 signal going to PLC-001 is not a correct symbol. It needs to be triangle shape like of LT-903.
(4) Don’t require 2 x LT on BOOT side. One LT should be enough to turn on or off the pump; also alarm can be set on the same LT.
(5) Some of the gas will bypass mist eliminator. As liquid level can only be maintained in boot section.
Please let me know if I am mistaking or is there any impact on process. As my PM do not want make any changes.
Thank you in advance