Water Flowrate In Piping Tee-Off

pipe flowrate tee off water

This topic has been archived. This means that you cannot reply to this topic.
10 replies to this topic
Share this topic:
| More

#1 Low

Low

    Junior Member

  • Members
  • 21 posts

Posted 13 February 2012 - 03:51 AM

Hi,

I would like to know how should I make a educated guess about whether my water flow rate at the outlet is sufficient.

Fluid: PCW
Temp: 12-15C
Pressure: 5 bar
flowrate in the main header, 16" = 300-400 m3/h

Final outlet pressure: 4 bar
Required flowrate: 1 m3/h

We are going to hot tap a 6" pipe and I am tasked to find out if a 1 1/2" hot tap would suffice. At the moment the plan is to tee off each 1 1/2" pipe to supply for 2 units, meaning each hot tap will be supplying two units.

From 1 1/2" the pipe will be reduced to 1/2", passing through a ball valve, and then finally the outlet would be 3/8". The required final flowrate for the 3/8" outlet is 1 m3/h, and the outlet pressure is about 4 bar.

From the mainline flowrate it would seem like enough but I would just like to make sure.

Just to add, everything is existing and the only part we are adding would be from the 1 1/2" pipe onwards.

So to conclude, I would like to know if my flowrate obtained from the 1 1/2" pipe is sufficient, or do we need a bigger pipe, and how did you come about getting the figure.

Appreciate the help.

#2 Low

Low

    Junior Member

  • Members
  • 21 posts

Posted 13 February 2012 - 07:32 PM

Also how do you calculate the flowrate in an equal tee? Divide the flowrate evenly? And for a reducing tee you divide it using the ratio of their radius? Because if I use this method I barely have enough water for less than a quarter of the plant, so something must be wrong with my calculations/assumptions.

#3 vikramltv

vikramltv

    Gold Member

  • Members
  • 52 posts

Posted 14 February 2012 - 12:02 AM

It will be better if you attach a scketch for you sceme elaborating your problem..

#4 Low

Low

    Junior Member

  • Members
  • 21 posts

Posted 15 February 2012 - 12:05 AM

Will do.

#5 breizh

breizh

    Gold Member

  • Admin
  • 6,735 posts

Posted 15 February 2012 - 01:00 AM

You can dowload from Internet a software called PSIM ( pump system improvement modeling tool ) which can support your query . As stated , you must define your sketch first.
Hope this helps

Breizh

#6 Low

Low

    Junior Member

  • Members
  • 21 posts

Posted 15 February 2012 - 04:41 AM

Sketch attached. Appreciate the help.

Attached Files



#7 Low

Low

    Junior Member

  • Members
  • 21 posts

Posted 17 February 2012 - 12:56 AM

Anyone know how to use the PSIM?

EDIT: I can't really define my sketch in the PSIM because it only allows 12 pipes and 24 junctions, and both upstream and downstream of each junction have to be defined. I don't think it's enough for me, unless I am doing this the wrong way. Forgive me, I have no prior experience with piping software.

Edited by Low, 17 February 2012 - 01:26 AM.


#8 breizh

breizh

    Gold Member

  • Admin
  • 6,735 posts

Posted 18 February 2012 - 01:46 AM

let you use the examples and manipulate the input data and run the program , you should understand (From simple to complicated ones).
For each pipe you need to provide diameter , rugosity , altimetrie .

It's really home work .

Breizh

#9 vikramltv

vikramltv

    Gold Member

  • Members
  • 52 posts

Posted 19 February 2012 - 10:48 PM

I have not used PSIM, But I had solved the similar problem with PIPENET that requires flow or pressure inputs at end points. It will size your line in design mode once you give the fitting , elevations and end point pressure/flow. get a copy of it and it will surely do wt you need..

#10 Low

Low

    Junior Member

  • Members
  • 21 posts

Posted 28 March 2012 - 07:31 PM

Hi guys thanks for the valuable input.

#11 S.AHMAD

S.AHMAD

    Gold Member

  • ChE Plus Subscriber
  • 786 posts

Posted 29 March 2012 - 03:05 AM

1. We need to know the piping configuration - pipe length, fittings, elevation etc
2. Use line pressure drop equation to determine the flow rate