Posted 13 February 2012 - 03:51 AM
Hi,
I would like to know how should I make a educated guess about whether my water flow rate at the outlet is sufficient.
Fluid: PCW
Temp: 12-15C
Pressure: 5 bar
flowrate in the main header, 16" = 300-400 m3/h
Final outlet pressure: 4 bar
Required flowrate: 1 m3/h
We are going to hot tap a 6" pipe and I am tasked to find out if a 1 1/2" hot tap would suffice. At the moment the plan is to tee off each 1 1/2" pipe to supply for 2 units, meaning each hot tap will be supplying two units.
From 1 1/2" the pipe will be reduced to 1/2", passing through a ball valve, and then finally the outlet would be 3/8". The required final flowrate for the 3/8" outlet is 1 m3/h, and the outlet pressure is about 4 bar.
From the mainline flowrate it would seem like enough but I would just like to make sure.
Just to add, everything is existing and the only part we are adding would be from the 1 1/2" pipe onwards.
So to conclude, I would like to know if my flowrate obtained from the 1 1/2" pipe is sufficient, or do we need a bigger pipe, and how did you come about getting the figure.
Appreciate the help.
I would like to know how should I make a educated guess about whether my water flow rate at the outlet is sufficient.
Fluid: PCW
Temp: 12-15C
Pressure: 5 bar
flowrate in the main header, 16" = 300-400 m3/h
Final outlet pressure: 4 bar
Required flowrate: 1 m3/h
We are going to hot tap a 6" pipe and I am tasked to find out if a 1 1/2" hot tap would suffice. At the moment the plan is to tee off each 1 1/2" pipe to supply for 2 units, meaning each hot tap will be supplying two units.
From 1 1/2" the pipe will be reduced to 1/2", passing through a ball valve, and then finally the outlet would be 3/8". The required final flowrate for the 3/8" outlet is 1 m3/h, and the outlet pressure is about 4 bar.
From the mainline flowrate it would seem like enough but I would just like to make sure.
Just to add, everything is existing and the only part we are adding would be from the 1 1/2" pipe onwards.
So to conclude, I would like to know if my flowrate obtained from the 1 1/2" pipe is sufficient, or do we need a bigger pipe, and how did you come about getting the figure.
Appreciate the help.
#2
Posted 13 February 2012 - 07:32 PM
Also how do you calculate the flowrate in an equal tee? Divide the flowrate evenly? And for a reducing tee you divide it using the ratio of their radius? Because if I use this method I barely have enough water for less than a quarter of the plant, so something must be wrong with my calculations/assumptions.
#3
Posted 14 February 2012 - 12:02 AM
It will be better if you attach a scketch for you sceme elaborating your problem..
#4
Posted 15 February 2012 - 12:05 AM
Will do.
#5
Posted 15 February 2012 - 01:00 AM
You can dowload from Internet a software called PSIM ( pump system improvement modeling tool ) which can support your query . As stated , you must define your sketch first.
Hope this helps
Breizh
Hope this helps
Breizh
#6
Posted 15 February 2012 - 04:41 AM
Sketch attached. Appreciate the help.
Attached Files
#7
Posted 17 February 2012 - 12:56 AM
Anyone know how to use the PSIM?
EDIT: I can't really define my sketch in the PSIM because it only allows 12 pipes and 24 junctions, and both upstream and downstream of each junction have to be defined. I don't think it's enough for me, unless I am doing this the wrong way. Forgive me, I have no prior experience with piping software.
EDIT: I can't really define my sketch in the PSIM because it only allows 12 pipes and 24 junctions, and both upstream and downstream of each junction have to be defined. I don't think it's enough for me, unless I am doing this the wrong way. Forgive me, I have no prior experience with piping software.
Edited by Low, 17 February 2012 - 01:26 AM.
#8
Posted 18 February 2012 - 01:46 AM
let you use the examples and manipulate the input data and run the program , you should understand (From simple to complicated ones).
For each pipe you need to provide diameter , rugosity , altimetrie .
It's really home work .
Breizh
For each pipe you need to provide diameter , rugosity , altimetrie .
It's really home work .
Breizh
#9
Posted 19 February 2012 - 10:48 PM
I have not used PSIM, But I had solved the similar problem with PIPENET that requires flow or pressure inputs at end points. It will size your line in design mode once you give the fitting , elevations and end point pressure/flow. get a copy of it and it will surely do wt you need..
#10
Posted 28 March 2012 - 07:31 PM
Hi guys thanks for the valuable input.
#11
Posted 29 March 2012 - 03:05 AM
1. We need to know the piping configuration - pipe length, fittings, elevation etc
2. Use line pressure drop equation to determine the flow rate
2. Use line pressure drop equation to determine the flow rate
Similar Topics
How To Handle Water Byproduct And Man Hydrolysis In The Dbp Solvent RoStarted by Guest_martzian_* , 20 May 2026 |
|
|
||
How To Estimate The Water Dewpoint From Heat And Mass Balance Of NaturStarted by Guest_krishnnaa26_* , 30 Apr 2026 |
|
|
||
Steam Carrying Liquid From The Sour Water Stripping TowerStarted by Guest_kaidlut_* , 12 Sep 2024 |
|
|
||
Compressor Selection Based On Flowrate & Compression RatioStarted by Guest_Dhams_* , 19 Jan 2026 |
|
|
||
Steam Pots Cyclic Pressure Pulsation And Water HammeringStarted by Guest_Abdelilah_* , 07 Dec 2025 |
|
|

FB