I have to write a procedure on the re commisioning of a ammonia bullet. It is none refrigerated and a volume of 630m3. A hydrotest will be done where after we will purge the tank with N2. I need some info on the procedure from the hydrotest to the filling of the bullet.
|

Re - Commissioning Of Ammonia Bullet
Started by chemest72, Mar 22 2012 07:19 AM
2 replies to this topic
Share this topic:
#1
Posted 22 March 2012 - 07:19 AM
#2
Posted 22 March 2012 - 08:04 AM
Chemest72,
Get the book 'Chemical and Process Plant Commissioning Handbook' by Martin Killcross.
Get the book 'Chemical and Process Plant Commissioning Handbook' by Martin Killcross.
#3
Posted 22 March 2012 - 08:36 AM
Chemest72:
You require a pre-commissioning procedure as well. You have to prepare the equipment for a commissioning first.
Things I would note down as requisites (after the hydrotest) for a pre-commissioning and commissioning of a pressurized ammonia storage tank are as follows:
You require a pre-commissioning procedure as well. You have to prepare the equipment for a commissioning first.
Things I would note down as requisites (after the hydrotest) for a pre-commissioning and commissioning of a pressurized ammonia storage tank are as follows:
- Drain, clean, and dry the vessel – internally and externally;
- Purge with dry nitrogen if vessel is still humid internally;
- Confined space entry visual inspection ;
- Employ tank’s mechanical calculations and fabrication drawings to verify that the tank is in acceptable mechanical condition to safely withstand the designated MAWP and MAWV of the vessel; also confirm that if there are any revisions to the original tank fabrication drawings, these same revisions are backed up with acceptable engineering calculations and approvals;
- Install all nozzle pipe connections, block valves, instruments, pressure relief valves, and alarms;
- Check out and calibrate – if necessary – all instruments and PSVs;
- Apply a pneumatic pressure test to the assembled tank with nitrogen and test for leaks at all connections and gaskets;
- After complying with above, fill the tank with the initial quantity of liquid ammonia after evacuating the nitrogen fill;
- Ensure that the liquid level, temperature, pressure instrumentation is working adequately and accurately and testing all alarm points where possible;
- Turn over commissioned tank to operations with a sign-off document.
Similar Topics
Ammonia Line Vapor GenerationStarted by Guest_simadri_* , 07 Apr 2025 |
|
![]() |
||
Ammonia Plant Start-Up ProcedureStarted by Guest_Baz_* , 08 Apr 2025 |
|
![]() |
||
![]() Ammonia Synthesis Loop SimulationStarted by Guest_Said Salim_* , 05 Apr 2017 |
|
![]()
|
||
![]() Ammonia Gas With WaterStarted by Guest_James Clerk Maxwell_* , 09 Sep 2024 |
|
![]() |
||
Analysis Of Ammonia Content In EthyleneStarted by Guest_Movers_* , 04 Jun 2024 |
|
![]() |