Sheiko,
For any flow transmitting instrument (or for that matter pressure transmitter etc), there is a maximum range that it can be used to measure. A flow meter, when procured, might have a maximum range of 0-2000 m
3/hr. This normally corresponds to 4-20 mA from the FT.
But as with other equipments, the range that you need in your process will not always match the standard equipment ranges sold by different manufacturers. For example, the above transmitter might have been procured to measure a flow in the range of 0-800 m
3/hr.
Normally, before shipping, the vendor would have re-ranged the instrument as per the datasheet sent to him (0-800 m
3/hr). Or otherwise, it would be re-ranged by plant instrument guys when it is installed first time around. The re-ranging is a straight forward procedure using industry standard communication methods like HART. This means the transmitter will send 4-20 mA in the range of 0-800 m
3/hr In the DCS too, the display would have been configured to show 0-100% as 0-800 m
3/hr. And usually in most cases, the specification sheet would show the same value.
Note now that there are three ranges:
1. The maximum range the instrument can physically measure (0-2000 m
3/hr)
2. The re-ranged instrument on installation (0-800 m
3/hr)
3. The DCS range (0-800 m
3/hr)
Ideally the installed range on instrument and DCS range should match.
Sometimes, due to many reasons, the range required by process will change. It might be during commissioning or after de-bottlenecking or plant revamp etc. In that case, the instrument will neeed to be re-ranged for the new required flow. The process department will send the request to plant instrument guys. For example, the new required flow might be 0-1000 m
3/hr.
This can still be measured by the same instrument, but would only need re-ranging in the field and re-ranging in the DCS. If the changes are not done in both places, you have problems. Sometimes (as is the usual case), changes would have been done in plant and DCS, but the paperwork would have gone missing, misplaced etc. The file might still show the earlier range.
Hope you have understood the bigger picture.
Check with the instrument manufacturer's website with the model number what is the absolute maximum range of the transmitter. Check with the instrument department what is the actual range of the instrument in the field and what is that in DCS. If all are matching, check what happend to the paperwork
Again this is a chemical engineer's understanding of how these things work. So take it in that light!!!