Please find attached an Excel Sheet wherein I have tried to calculate the Venting capacity of Pressure Safety Valve for Double wall double integrity Ammonia Storage Tank. I tried to calculate the capacity of Venting as per API-2000 for the case when there is fire around the Tank. Calculation have been done for FPS and SI unit system. However, both the answer are different. I am not able to spot the error in my calculation. I am also not sure whether my calculation is correct. Please guide me in correcting the Excel sheet.
Alok
#2
Posted 23 August 2012 - 06:01 AM
Alok
Attached Files
#3
Posted 02 December 2012 - 01:20 PM
Dear all,
Please find attached an Excel Sheet wherein I have tried to calculate the Venting capacity of Pressure Safety Valve for Double wall double integrity Ammonia Storage Tank. I tried to calculate the capacity of Venting as per API-2000 for the case when there is fire around the Tank. Calculation have been done for FPS and SI unit system. However, both the answer are different. I am not able to spot the error in my calculation. I am also not sure whether my calculation is correct. Please guide me in correcting the Excel sheet.
Alok
Dear Alok,
I do think the mistake is due to the units of vaporization heat in SI (cell I12 of your spreadsheet). Vaporization heat in the API 2000 formula is in J/kg, not in kJ/kg. You have to multiply by 1000 the vaporization heat value.
Cheers
Stefano
#4
Posted 05 December 2012 - 02:17 AM
1. British Unit
W = 64431391 x 0.05 / 587.826 =5480.5 lb/h or 2485.5 kg/h
2. SI Unit
W =(18882626/1000) x 3600 x 0.05 / 1367.283 = 2485.85 kg/h
3. Even-though not exactly the same but very close
4. Pls take note that your equation for NM3 conversion is incorrect.
Edited by S.AHMAD, 05 December 2012 - 02:24 AM.
Similar Topics
![]() Storage Tanks Diked Area Fire Protection Using Foam MakerStarted by Guest_mkhattaby_* , 30 Jan 2025 |
|
![]() |
||
Fire Relief Case - Relieving TemperatureStarted by Guest_alexzo1990_* , 06 Nov 2024 |
|
![]() |
||
Maximum Velocity For Piping In Fire Water Distribution System (Fire WaStarted by Guest_applepe_* , 06 Sep 2024 |
|
![]() |
||
![]() Determining The F-Factor Following The Api 2000Started by Guest_Hachimi_* , 06 Sep 2024 |
|
![]() |
||
![]() Fire Case Gas Expansion (Gas Filled & No Liquid)Started by Guest_moosa.akbar_* , 27 Aug 2024 |
|
![]() |