Two Phase Reverse Flow -Psv Sizing For Check Valve Failure Case


3 replies to this topic
Share this topic:
| More

#1 namita.modak1

namita.modak1

    Brand New Member

  • Members
  • 1 posts

Posted 01 April 2026 - 08:15 AM

We have a Vaccum Pump Downstream of which it is two phase and check valve is given on discharge line going to Separator.

On discharge line PSV is provided for a set pressure of 1.3 barg whereas the Separator design pressure is 14 barg.We have strainght guideline in API for single phase check valve failure case but not for Two Phase.Can you please guide how to estimate relief load.



#2 Pilesar

Pilesar

    Gold Member

  • Admin
  • 1,645 posts

Posted 01 April 2026 - 11:38 AM

I think you are saying that the line has two-phase flow under normal conditions. Will it still be two-phase under relief conditions? 



#3 latexman

latexman

    Gold Member

  • Admin
  • 1,896 posts

Posted 02 April 2026 - 05:39 AM

Can you please guide how to estimate relief load.

 

Usually, to be conservative on relief sizing, homogeneous two phase flow is assumed.



#4 breizh

breizh

    Gold Member

  • Admin
  • 6,953 posts

Posted 02 April 2026 - 07:49 AM

A few documents for sizing PSV -two phases flow.

What is scenario, check valve failure? What said the Hazop study to mitigate the risk? dual check valves? drawback head loss!

Good luck

Breizh