I wonder if anyone can help me with this. I am looking to calculate the required rate of fuel gas purge used in a cold vent header open to atmoshere. So far the only information i have come across is relating to flare stacks (API 521). Can the formulas be applied to fuel gas purge of cold vents?
If not can you link to me any literature with formulas specifically used for calculating the puge rate of cold vent headers?
Thanks,
|

Using Fuel Gas For Continuous Purge Of Cold Vent
Started by Wiseguy007, Nov 29 2012 12:31 PM
3 replies to this topic
Share this topic:
#1
Posted 29 November 2012 - 12:31 PM
#2
Posted 29 November 2012 - 08:02 PM
My first job more than 40 years ago was in an ethylene unit with cold vents. We never used purge. But the vents had a vent head with a steam ring.
Bobby
Bobby
#3
Posted 30 November 2012 - 10:51 AM
It is a vent system with several process lines feeding into it; these then lead to the vent knock-out drum with open vent open to atmosphere.
Purge gas is taken directly from the production header and used for continuous purge.
Is there a minimum requirement for purge rates in any of the API standards?
Does anyone have any ideas on how to proceed with this calculation?
Purge gas is taken directly from the production header and used for continuous purge.
Is there a minimum requirement for purge rates in any of the API standards?
Does anyone have any ideas on how to proceed with this calculation?
Edited by Wiseguy007, 01 December 2012 - 05:10 AM.
#4
Posted 02 December 2012 - 11:49 PM
hi
i was looking at this thread and expected some senior guys to comment/advice the OP.
my questions and thoughts are:
1) is it existing one or are you designing new one?
2) who suggested FG purging for a cold vent?
3) know the difference between the functionality of a cold vent and a flare ( Hint: cold vent is for intermittent instant relief! and not for continuous flow)
4) purging of cold vent is done with non-combustible (N2) to prevent air
5) always remember cold vent is a possible source of fire; that is why API talks of radiation assuming a fireball incident and dispersion using DEGADIS or some such software; and check NFPA 211.
6) Finally look at your operator company; what is their hse recommendations regarding cold vent. are they willing to cover insurance for cold vents?
regards
neelakantan
i was looking at this thread and expected some senior guys to comment/advice the OP.
my questions and thoughts are:
1) is it existing one or are you designing new one?
2) who suggested FG purging for a cold vent?
3) know the difference between the functionality of a cold vent and a flare ( Hint: cold vent is for intermittent instant relief! and not for continuous flow)
4) purging of cold vent is done with non-combustible (N2) to prevent air
5) always remember cold vent is a possible source of fire; that is why API talks of radiation assuming a fireball incident and dispersion using DEGADIS or some such software; and check NFPA 211.
6) Finally look at your operator company; what is their hse recommendations regarding cold vent. are they willing to cover insurance for cold vents?
regards
neelakantan
Similar Topics
![]() Free Vent For Api 650 Tank - Bug Screen / Bird Screen RequirementStarted by Guest_Cabbarbeybaba_* , 03 Jul 2025 |
|
![]() |
||
Improving Safety By Re-Routing Priming Vent Line In Centrifugal Pump HStarted by Guest_Srinivas Agastheeswaran_* , 31 Jan 2025 |
|
![]() |
||
Psv On Ko Drum With Flame Arrestor At Flare Vent LineStarted by Guest_Tintin2024_* , 29 Oct 2024 |
|
![]() |
||
Effect Of Continuous Blow Down To Boiler Feed WaterStarted by Guest_Dyames027_* , 21 Nov 2024 |
|
![]() |
||
Sugar Impurities After Distilling Ethanol FuelStarted by Guest_vyse_* , 14 Nov 2024 |
|
![]() |