Psv On Ko Drum With Flame Arrestor At Flare Vent Line


3 replies to this topic
Share this topic:
| More

#1 Tintin2024

Tintin2024

    Brand New Member

  • Members
  • 1 posts

Posted 29 October 2024 - 08:44 AM

Hello,

 

I have a section VIII KO drum with no PSV on it. My understanding is that as long as there is no overpressure or there is vent line, the KO drum typically does not need a PSV on it. However, this KO vent to a flare stack. And along the vent line, there is a flame arrestor. Per API 14C, a flame arrestor is considered an obstruction, and a PSV should be installed on the KO drum. 

 

The problem I am facing is that API 14C is written for offshore facilities. We are not offshore. Is there any API equivalent for onshore? Should we consider PSV on this KO Drum? We have some BDVs with upstream pressure going up to 1200 psig, exceeding the KO drum MAWP. 



#2 fallah

fallah

    Gold Member

  • ChE Plus Subscriber
  • 5,019 posts

Posted 29 October 2024 - 02:21 PM

Hello,

 

I have a section VIII KO drum with no PSV on it. My understanding is that as long as there is no overpressure or there is vent line, the KO drum typically does not need a PSV on it. However, this KO vent to a flare stack. And along the vent line, there is a flame arrestor. Per API 14C, a flame arrestor is considered an obstruction, and a PSV should be installed on the KO drum. 

 

The problem I am facing is that API 14C is written for offshore facilities. We are not offshore. Is there any API equivalent for onshore? Should we consider PSV on this KO Drum? We have some BDVs with upstream pressure going up to 1200 psig, exceeding the KO drum MAWP. 

 

If vent to flare network, no need to apply flame arrestor.



#3 shvet1

shvet1

    Gold Member

  • Members
  • 457 posts

Posted 31 October 2024 - 12:21 AM

1/ Please describe this flame arrestor

2/ Is the pressure in this PV self-limiting? Does this PV have records of "overpressure protection by system design" as per ASME XIII or relevant chapters in withdrawn issues of ASME VIII?

3/ Is this PV considered as a "dry vessel" as per API 521?

 

 

 Is there any API equivalent for onshore?  

 

No. ASME&API have no such


Edited by shvet1, 31 October 2024 - 04:10 AM.


#4 Sawsan

Sawsan

    Brand New Member

  • Members
  • 2 posts

Posted 02 December 2024 - 03:59 AM

flame arrestor poses risks of obstruction negating its purpose in flashback deflagration protection. 

Please refer to API 14J for flashback protection where flare KO drum design pressure (which floats with flare) needs to be designed for a minimum of 125 Psig to mitigate flashback deflagration consequent risks. Protecting from detonation can only be mitigated by propoer puging with inert nitrogen to eliminate flammable mixture to fall withing LEL and UEL. 

 