I have seen only sketch 1 in refinery PIDs, it must be more common as pointed out by Fallah. An explanation is that process stream flow had better be more or less constant in most cases. On the other hand cooling water network is complex, so that variation in one cooling stream would not be "sensible". This is also valid for steam networks and other refinery utilities.
Even reduction of total CW return to cooling tower (within limits, not to cause e.g. channeling in tower or scales in the pipe) will not have an undesirable effect. For instance, consider hot water temp=100 oF, air wet bulb=70 oF. Perry's Fig 12-14 (7th edition, 1997, Mechanical Draft Towers) indicates cold water temp of 80 oF for "water concentration" = 2.5 gal/min/ft2, or 76 oF for 1.5 gal/min/ft2 (40% reduction in CW flow).