hi everyone,
I am designing dew point heater(electric heater type). The process flow of the natural gas sytem is as follows:
KO drum - Natural Gas Metering station - Dew point heater - pressure reducing station - absolute seperator - performance heater - scrubber - Gas Turbine
The interface point from our client is after Natural Gas Metering Station.
The interface Natural Gas conditions are:
Pressure : 29 bar A to 73 bar A
Temperature : 10 to 45 deg C
flow: 31220 kg/hr
The fuel gas composition is as follows:
methane(90.066%), ethane(4.566%),Propane(0.236%), n-Butane(0.018%),Isobutane(0.018%),n-Pentane(0.007%),Isopentane(0.007%),n-Hexane(0.002%),Nitrogen(5.025%),Carbon Dioxide(0.055%),HHV (kJ/kg)-50,629,LHV (kJ/kg)-45,694,Specific Gravity-0.6
The above composition is volume basis.
The pressure required at the inlet of Gas Turbine(as per gas turbine vendor) is 33 bar A.
We have to size only the Dew Point heater.
The temperature after performance heater is fixed. It is 152 deg.C, during normal operation.
Gas Turbine vendor states that " the natural gas temperature shall be atleast 28 deg.C above dew point temperature after performance heater, to avoid condensate formation".
During normal operation, there is no problem. As the temperature after performance heater is 152 degC, the Gas turbine vendor requirement is satisfied.
But during startup, the performance heater will be bypassed. Hence during startup dewpoint heater is required to fulfill the requirement of Gas Turbine vendor(i.e gas temperature atleast 28 degC above the dew point)
Considering maximum Natural Gas pressure(73 bar A) at the inerface, the pressure is to be reduced to 33 bar A.(as required by the Gas turbine vendor) by pressure reducing station.
For every 1 bar A decrease in pressure, the temperature decreases by 0.6 deg.C(as given by Gas Turbine vendor), hence the temperature decreases by 24 deg.C.
Considering dew point of 0 deg.c(not known only assumption), the temperature at the outlet of dew point heater shall be 52 degC(0 degC + 28 deg C+ 24 degC). This is only during startup when performance heater is bypassed.
During normal operation, dew point heater can be bypassed.
My questions are
1. How can we calculate the dew point of natural gas. Iam using hysis but donot know how to calculate dew point. Or is there another way of calculating dewpoint.
2.Is there any problem if we place dewpoint heater after absolute seperator, please tell the advantages
of placing dew point after absolute seperator.
Thanks in advance.