I have one query on the Centrifugal Compressor blocked outlet scenario.
Please refer attached sketch.
This is regarding Centrifugal compressor operating on the onshore oil and gas separation facility (in design/Feed stage).
As per blocked outlet scenario, the blocked outlet flow rate for the PSV-101 is 12.5 MMSCMD (set at 4200 kpa). However, this new compressor will be connected to existing flare system which has maximum capacity of 8 mmscmd.
Therefore, in the feed document, one additional PSV-102 (“Recycle PSV”) is provided downstream of air cooler, which is set at slightly lower set pressure (3990 kpa) . But this PSV discharge back to inlet of the suction scrubber. This PSV (PSV-102) sized for 4.5 mmscmd and PSV-101 is for 8 mmscmd. This way feed contractor has justified that maximum 8 mmscmd flow will go to the flare.
I am not able to understand how this arrangement will help to provide enough protection in the compressor blocked outlet scenario.
I'd be glad if any one share his opinion/experience.

FB