on the relief valve bypass, there is a spectacle blind. Is there a code which states the position (open or close) of the spectacle blind.
Thank you.
|
Posted 29 July 2013 - 03:35 PM
on the relief valve bypass, there is a spectacle blind. Is there a code which states the position (open or close) of the spectacle blind.
Thank you.
Posted 30 July 2013 - 01:06 AM
syn23,
As far as i know there is no need to consider spectacle blind in PSV by pass line, because the PSV set including PSVs, isolation valves, by pass line and valve are to be isolated positively from upstream vessel by a spool piece. The spool piece will be used instead of spectacle blind due to safety issue...
Posted 30 July 2013 - 07:49 AM
Syn23,
Agree with Fallah, spec blind is not required if the valve holds good. So I think this spec blind is provided for positive isolation and to have PSV in service all the time. Therefore the spec shall be in closed position all the time.
Posted 30 July 2013 - 09:17 AM
Posted 30 July 2013 - 10:59 AM
Thank you all for your response,
I agree that it should be left in CLOSE position.
I just found out the client preference, is to leave the blind in OPEN position. I was looking to see if there is any API code to dictate the requirement so that it will be a valid argument. Otherwise, its just "we want it this way".
Posted 30 July 2013 - 11:41 AM
syn23,
Client preference, to leave the blind in OPEN position, shows there might be a case he needs using the by pass line durnig normal operation. Suppose for the PSV configuration, appears to be for only fire case (because of single PSV), there would be a situation that the PSV should be taken out of service in order to be repaired or inspected and puting the spare might take a lot of time. Then the operator have to rely on by pass line during the time the PSV is out of service and a safety issue might be probable during the time between taking PSV and puting the spare. For your information there is a procedure well defined in ASME sec VIII by which it might possible taking a single PSV out of service for a short time in normal operation.
Therefore IMO if you have to use spectacle blind there, i agree with your client to keep it in open position during normal operation...
Posted 31 July 2013 - 12:43 AM
Posted 31 July 2013 - 12:53 AM
Posted 04 February 2014 - 07:47 AM
Bypass line is not mandatory for all PSVs were there is a line routed to flare or ATM from top of the vessel or column. Like with pressure control adustment to falre/ATM or gas blanketing facility (In-breathing and out breathing).This line can be used for depressurisation bebore planned maitenanace.
![]() Isolation Requirement For Bypass Valves/ Movs.Started by Guest_shantanu.ghag_* , 15 Sep 2024 |
|
![]() |
||
![]() Bypass Line Control LoopStarted by Guest_Tee2012_* , 20 Aug 2024 |
|
![]() |
||
![]() Bypass Line SizeStarted by Guest_Fatima105_* , 09 Feb 2023 |
|
![]() |
||
![]() ![]() Psv Bypass Line SizeStarted by Guest_R_Gowtham_* , 06 Jun 2022 |
|
![]() |
||
![]() Hot Bypass With Pressure Differential ValveStarted by Guest_Venkat @89_* , 03 Dec 2022 |
|
![]() |