For two phase relief valve sizing, we have used HEM method and in datasheet we have reported properties at maximum mass flux. Now in aspen flarnet software, shall we give this properties or proerties at relieving condition for network analysis. Because based on this, psv outlet properties will change. Please suggest.
#2
Posted 07 November 2013 - 06:58 AM
when a PSV discharges on a flare (network) normally
I run a software (to simulate the network, calculate
back pressures on each PSV etc.etc.)
with flows and conditions at relieving condition
for a specific case
(i.e. fire, some accident etc.) , there could be
several cases to examine and, of course,
one selects as design case that with maximum flows,
pressure drops etc. etc. on flare netwrok,
I have not experience with large networks
(I have PRODE PROPERTIES which
includes HEM model for PSV and piping
but not a solver fro networks,
so I have my own solver)
however I suppose the procedure is the same.
#3
Posted 07 November 2013 - 07:38 AM
#4
Posted 07 November 2013 - 08:12 AM
does not Flarenet manual specify
which properties the software require ?
I have not Flarenet,
if the above (consider flows and conditions
at relieving conditions for each specific case
i.e. fire, some accident etc.)
doesn't help I suppose you need
the details about how to enter
the values in the sofware,
usually these are discussed in the manual
and I would be surprised should it not clarify
this point,
Flarenuf or other experts here may adise.
Edited by PaoloPemi, 07 November 2013 - 08:41 AM.
#5
Posted 09 November 2013 - 02:41 AM
abhijit
good question !
the problem here is that generally when people use flarenet they use the properties of the fluid in the pSV at design conditions. ie the values used to size the psv
this will usually be at accumulation pressure values.
in reality the flow, temp and pressure at relieving conditions with the actual selecetedlarger orifice size will be different and in most cases the relieving pressure will be less than the design relieving pressure.
so which figs do you use ..
if this is the only PSV relieving in a scenario then you should use the max mass flow to give you the better backpressure calc in fnt
if however this is only one of many PSV's releiving in a scenario then you could be using a mix of max mass flow for this pSV and design values for the other flows.
if it is 1 of many then look at the contribution of this PSV to the total scenario load, is it 5% or 75% what impact does it have on the backpressures in the network?
run fnt with your max mass flow and design flow and see if there is any noticeable difference in teh calculated results
if not then fine , if it does have an impact then its down to engineeering judgement to determine the way forward.
probably not the " use this figure" answer you wanted but without the whole picture i cannot be more definitive
look at the impact of either way and decide ...
flarenuf
Similar Topics
Heat Exchanger Steam FlowStarted by Guest_aliebrahem17_* , 25 Nov 2024 |
|
![]() |
||
![]() Flow Through Normally No Flow LineStarted by Guest_iippure_* , 08 Apr 2025 |
|
![]() |
||
![]() Flare Header Reverse FlowStarted by Guest_Ahmadhamzahperta_* , 04 Apr 2025 |
|
![]() |
||
![]() Dynamic Simulation After Feed Flow ReductionStarted by Guest_Kakashi-01_* , 20 Mar 2025 |
|
![]() |
||
Modeling Liquid Metals In Aspen PlusStarted by Guest_AnthonyB_* , 03 Apr 2025 |
|
![]() |