What air flow does Hysys calculate?
Air flow required depends on number of theoretical stages in the column. With 3 stages less air is required than with 2 stages.
Obviously the air leaving the column at the top can not be warmer than the incoming water, which is at 45 oC.
Let's assume that a realistic air outlet temperature is 40 oC, then the maximum possible water content of that air can be calculated using a steam balance.
You know the water content of the air entering the column.
You can also calculate the duty of the cooling tower from the cooling water flow rate and the inlet and outlet temperatures.
Using the heat of vaporization of water you can estimate how much water has to vaporize.
Then finally you can calculate how much air is required to carry that amount of water vapor out of the column.