Dear all,
I wish to design a pressure relief valve for a reactor having independent bursting disc both discharging to a vessel having open vent.
- The valve is designed for vapour release for external fire case.
- Set pressure is 2barg and design pressure of vessel is 6barg
- Overpressure allowed is 10% of set pressure
- For external fire case, the vapour release rate is 5000kg/hr and for this release rate, minimum area required is 1225mm2 [I have calculated this area using equation Kd A = Q /(Po. C. SQRT(M/(Z.To)))]
- From API standard, I have selected orifice ‘L’ which equates the vent area of 1841mm2. I have back calculated the maximum capacity with this area and is about 7000kg/hr
I have few queries as below please.
- I believe, the overpressure allowance should be 21% as the valve is designed for fire case. Do you think, we can design a valve with 10% overpressure for external fire case?
- If I allow 21% overpressure, I believe, I need to limit the back pressure to 21% and not 10%. Please correct me if I am wrong.
- Also to check the valve discharge line back pressure, I believe, I need to calculate pressure drop for the flowrate of 7000kg/hr and NOT 5000kg/hr. Please comment/correct.
- What would be the total back pressure [i.e. superimposed + built up back pressure] ? For example the calculated pressure drop at the valve discharge line for the release rat of 7000kg/hr is 0.2bar and as the line is open to vessel with open vent, can I say the back pressure is only 0.2barg and is OK as it’s 10% of 2barg? Please comment.
Thanks in advance.