These phosphate values are very high for that pressure.
See Phosphate Continuum Treatment (former EPT) in EPRI guidelines.
Do not inject TSP in feedwater (FW).
The maximum recommended value is 20 ppb hydrazine in FW. It is generally used when copper metallurgy (see document 3).
Documents:
1) Cycle Chemistry Guidelines for Combined Cycle/Heat Recovery Steam Generators (HRSGs).
EPRI, Palo Alto, CA: 2006. 1010438.
2) Cycle Chemistry Guidelines for Fossil Plants: Phosphate Continuum and Caustic Treatment,
EPRI, Palo Alto, CA: 2004. 1004188.
3) Guidelines for Controlling Flow-Accelerated Corrosion in Fossil and Combined Cycle Plants,
EPRI, Palo Alto, CA: 2005. 1008082.
Edited by mario_1970, 04 June 2014 - 09:16 AM.