I have a question for providing overpressure protection for custody metering skid as per ASME B31.8 code, para 845.2.4
Does it mandatory to provide slam shut off valve along with active monitor regulator configuration and redundant safety relief valves? Existing skid has been designed and built with active monitor regulator configuration and redundant safety relief valves. Operations is adamant and asks us to provide slam shut off valve. Please advise me if existing arrangement of two regulators in series and safety relief valve is adequate or not for over pressure protection of piping.
Highpressure distribution system.
Suitable types of protective devices to prevent overpressuring
of high-pressure distribution systems
include
(1) relief valves as prescribed in paras. 845.2.1(a)
and (
(2) weight-loaded relief valves
(3) a monitoring regulator installed in series with
the primary pressure regulator
(4) a series regulator installed upstream from the
primary regulator and set to limit the pressure on the
inlet of the primary regulator continuously to the maximum
allowable operating pressure of the distribution
system or less
(5) an automatic shutoff device installed in series
with the primary pressure regulator and set to shut off
when the pressure on the distribution system reaches
the maximum allowable operating pressure or less. This
device must remain closed until manually reset. It
should not be used where it might cause an interruption
in service to a large number of customers.
(6) spring-loaded, diaphragm-type relief valves