Dear Experts,
I'm a junior process engineer doing relief calculations for an MTBE vaporizer. Here's the background of the process:
Subcooled MTBE is pumped to a heat exchanger (shell side, DP = 17.5 barg) where it undergoes heating, vaporization, and superheating all in one shell. This is done using a 25 barg steam (tube side, DP = 30 barg). The superheated MTBE goes to a reactor section (DP = 17.5 barg) afterwards to undergo a vapor-phase reaction converting it to Isobutylene. Afterwards, it is cooled using a series of coolers (DP = 17.5 barg). A PSV protects the vaporizer with a set pressure of 17.5 barg. The normal operating pressure in the vaporizer is 10 barg. (SEE ATTACHED SKETCH) MTBE VAPORIZER.PNG 46.33KB 3 downloads
Here are my two main problematic scenarios (apart from common ones like fire):
(a) blocked discharge - 40 tons/hr
( tube rupture - 120 tons/hr
The relief load calculated is based on the assumption that all of the heat that can go in the exchanger is taken to vaporize a potentially infinite liquid pool on the exchanger (since the feed pump can supply enough pressure to deliver MTBE during relief conditions).
The concern is that we are limited to only 14 tons/hr. For this specific project, we take credit for SIS action and we intend to use a high pressure trip that closes the steam supply via SIS. This reduces the heat input to a minimal amount (only a small flow from the leakage through the steam valves) .
Unfortunately, when we generated a pressure vs time analysis, it takes only 5 seconds to reach the relief pressure. The fastest response time we have available is 10 seconds (from detection to valve closure).
Now, I'm considering the use of a rupture disc which would be piped towards an upstream tower (volume = 165m³) with a design pressure of 6 barg. I am concerned however, about how much depressurization can I really get away with.
Any ideas/comments/suggestions? I would appreciate them