|


Prv Fire Case Load Calculation For Mixture.
#1
Posted 24 June 2024 - 11:55 AM
#2
Posted 25 June 2024 - 12:40 AM
you can adopt some "conservative" estimate (see API etc.) or try to solve phase equilibria + heat balance, several tools available, see for example this previous thread :
https://www.cheresou...ure-using-hysys
#3
Posted 25 June 2024 - 12:20 PM
You may find useful discussion from several years ago: https://www.cheresou...f-vaporization/
#4
Posted 29 June 2024 - 01:48 AM
Please share your engineering practice or opinion on this case.
For such cases we use equilibrium vapor composition at relieving pressure
#5
Posted 29 June 2024 - 05:41 AM Best Answer
Please share your engineering practice or opinion on this case.
We use the component with the lowest heat of vaporization. It is simple and conservative.
#6
Posted 08 July 2024 - 12:36 PM
Dear All,
Sorry for the late response and thanks for every comments.
I solved this problem with using the component with the lowest heat of vaporization.
Even assuming relieving component as TEG, it didn't cause any major concerns.
Similar Topics
Is Emergency Venting Required For Polyethylene Storage Tank In Fire ScStarted by Guest_chem55_* , Yesterday, 03:06 PM |
|
![]() |
||
![]() Heat Loss Calculation From Cylindrical Tan;Started by Guest_rasprocess2026_* , 23 Jul 2025 |
|
![]() |
||
![]() Relief Path To Be Considered For Inlet Pressure Drop CalculationStarted by Guest_Ascanio E._* , 09 Jul 2025 |
|
![]() |
||
![]() ![]() Nozzle Sizing CalculationStarted by Guest_BabRafiq1_* , 26 Aug 2022 |
|
![]() |
||
![]() Api Calculation In HysysStarted by Guest_phoroogh_* , 22 Feb 2025 |
|
![]() |