Hi Engineers,
May I seek your guidance on the following?
I have a vertical vessel that is fully filled with water containing a trace amount of hydrocarbon. Due to a device located near the top dished head, the pressure relief valve (PRV) cannot be installed at the top and must instead be located on the side of the vessel, below the liquid level.
Per API 521, when a PRD is located below the liquid level of a vessel exposed to fire, the PRD should be capable of relieving a volume of fluid equivalent to the volume of vapor generated by the fire. It is also stated that two‑phase PRD sizing is generally not required for fire cases, except for unusually foamy materials or reactive chemicals.
In this case, how should the PRD be sized? If the relief device is installed on the vessel shell well below the liquid level, or on a liquid feed line, the relieving fluid under fire exposure would be liquid. If the vapor generation rate is used to drive the equivalent liquid flow rate, would this not result in an oversized PSV?
On the other hand, if only vapor generation is considered, there is a concern that the valve may be undersized.
I would appreciate your advice on the appropriate sizing approach for this scenario.
Thank you for your time and support.
|
|
Sizing Fire Case Relief Valve Installed Below Liquid Level
#1
Posted Today, 10:17 AM
#2
Posted Today, 12:16 PM
Per API 521, when a PRD is located below the liquid level of a vessel exposed to fire, the PRD should be capable of relieving a volume of fluid equivalent to the volume of vapor generated by the fire.
Did you not answer your own question? I do not understand why this is not satisfactory to you. Have you calculated the fire case vapor generation rate for a vertical vessel containing water?
#3
Posted Today, 12:36 PM
Per API 521, when a PRD is located below the liquid level of a vessel exposed to fire, the PRD should be capable of relieving a volume of fluid equivalent to the volume of vapor generated by the fire.
Did you not answer your own question? I do not understand why this is not satisfactory to you. Have you calculated the fire case vapor generation rate for a vertical vessel containing water?
#4
Posted Today, 02:33 PM
Your situation is curious with a completely filled water pressure vessel with no vapor space at all. If the normal inlet or exit of the vessel is not blocked in, the fire case can consider those paths as a relief exit. Completely blocking in a filled water vessel with no vapor space is an additional relief scenario you must consider anyway due to thermal expansion. Why not just put the PRD near the bottom of the liquid? Is there no bottom nozzle?
I think there must be more to this situation that you have revealed. If the vessel has no PRD now, then it must be in the design phase where you are determining where to install the vessel nozzle for a PRD. We do not know the size, pressure, function, etc of the vessel. It sounds like an interesting problem!
#5
Posted Today, 03:15 PM
Allow me to briefly provide the relevant information:
- Equipment: Hydrocyclone (vertical)
- Vessel diameter: 1.0 m
- Tangent‑to‑tangent height: 1.4 m
- Head: 2:1 ellipsoidal
- Set pressure: 30 barg
That said, may I ask how locating the PRD near the bottom of the liquid would be beneficial? Also, please excuse my naïve question: according to API 521, when a PRD is located below the liquid level in a vessel exposed to fire, the PRD should be capable of relieving a volume of fluid equivalent to the volume of vapor generated by the fire. In this context, do we assume that the required liquid volumetric flow rate is equal to the volumetric rate of vapor generation due to the fire?
Similar Topics
Two Phase Reverse Flow -Psv Sizing For Check Valve Failure CaseStarted by Guest_namita.modak1_* , 01 Apr 2026 |
|
|
||
Steam Carrying Liquid From The Sour Water Stripping TowerStarted by Guest_kaidlut_* , 12 Sep 2024 |
|
|
||
Free Pump Sizing Calculator For Preliminary Engineering ChecksStarted by Guest_Gonoklab_* , 16 Mar 2026 |
|
|
||
Conceptual Sizing Of Adsorber ColumnStarted by Guest_JJvdM_* , 24 Oct 2019 |
|
|
||
Free Pump Sizing Calculator For Preliminary Engineering ChecksStarted by Guest_Gonoklab_* , 16 Mar 2026 |
|
|

FB