Need assistance on selection of design Cv for pressure control valve based on calculated Cv
|

How To Select Control Valve Design Cv Based On Calculated Cv
#1
Posted 02 May 2014 - 03:10 AM
#2
Posted 02 May 2014 - 07:57 AM
The rule of thumb was always to aim to select a valve that would have the calculated Cv when about 70% open. Obviously valves go up in step sizes so you cannot get it to be exactly 70%. Of course it will also depend on your process variability. The design Cv is calculated on 1 point. If you know the process will often deviate from that design point then you should include that information in your decision.
If the full-open Cv of the valve is too small to cope with process extremes how dangerous does the deviation become?
In the "old days" it was often found that if the valve was too big, and therefore operated towards the closed end of its range, then the control system would "hunt" and not reach a steady state. With modern valve positioners and self-tuning controllers this is much less of a problem and I have seen valves run rock steady at 10% open.
Use the rule of thumb as a starting point and take the process circumstances into account to come to a reasoned selection. You may find that the valve supplier will be able to give relevant advice as well.
#3
Posted 02 May 2014 - 02:16 PM
Nikhilbha,
Please provide available process data to help you with numbers.
Regards.
Ajay
#4
Posted 03 May 2014 - 03:22 AM
Hi ,
Probably good to read !
Hope this helps.
Breizh
#5
Posted 15 May 2014 - 04:58 AM
Similar Topics
![]() Scrubber DesignStarted by Guest_nasss_* , 07 Aug 2024 |
|
![]() |
||
Critical Pressure For Choke Valve SizingStarted by Guest_Sherif Morsi_* , 07 Nov 2017 |
|
![]() |
||
Refinery Lpg Deethanizer Column DesignStarted by Guest_Ilyes_* , 15 Feb 2025 |
|
![]() |
||
Check Valve FailureStarted by Guest_Falah_* , 26 Mar 2025 |
|
![]() |
||
Alkaline Electrolytic Cell/stack Sizing/design For H2 ProductionStarted by Guest_BRS09_* , 13 Mar 2025 |
|
![]() |