API 521 states an equation to calculate the orifice size of a PRD, the discharge areas for PRDs on vessels containing supercritical fluids, gases or vapors exposed to open fires.

 

The question is, how to size the tailpipe or discharge piping, given that with this method, there is no load calculation (mass flow)?

 

 

 



#2 Bobby Strain

Bobby Strain

    Gold Member

  • Members
  • 3,529 posts

Posted 27 May 2014 - 06:40 PM

You should tell us what a PRD is. You use strange terminology. Assuming that it is a relief valve, when you have the orifice area, you can calculate the flow rate. But you probably already knew that.

 

Bobby



#3 wenchop

wenchop

    Veteran Member

  • Members
  • 33 posts

Posted 28 May 2014 - 06:37 AM

Strange terminology?
 
API 521 6TH EDITION quotes:
"The discharge areas for PRDs on vessels containing supercritical fluids, gases or vapors exposed to open fires can
be estimated using Equation"
 
Page 11 acronyms and abbreviations of API 521:
PRD pressure-relief device

Edited by magonz, 28 May 2014 - 06:51 AM.


#4 fallah

fallah

    Gold Member

  • ChE Plus Subscriber
  • 5,019 posts

Posted 28 May 2014 - 07:19 AM

API 521 states an equation to calculate the orifice size of a PRD, the discharge areas for PRDs on vessels containing supercritical fluids, gases or vapors exposed to open fires.

 

The question is, how to size the tailpipe or discharge piping, given that with this method, there is no load calculation (mass flow)?

 

 

magonz,

 

The fire relief load should has been calculated based on the procedure included in API 521. Then the PRD sizing would be performed using "Flow Resistance Method" included in API 520 part I (as attached) which appears to be same as what you quoted from API 521 6TH Ed. 

Attached Files



#5 wenchop

wenchop

    Veteran Member

  • Members
  • 33 posts

Posted 28 May 2014 - 07:28 AM

Exactly which procedure included in API 521, what page?



#6 fallah

fallah

    Gold Member

  • ChE Plus Subscriber
  • 5,019 posts

Posted 28 May 2014 - 10:57 AM

magonz,

 

At the moment i haven't API 521 in hand, but for one who is a little bit familiar with this standard it isn't so hard finding "Relief Load Determination" for pool fire...



#7 wenchop

wenchop

    Veteran Member

  • Members
  • 33 posts

Posted 28 May 2014 - 12:30 PM

If it is so easy, I will gladly await for the page number..



#8 fallah

fallah

    Gold Member

  • ChE Plus Subscriber
  • 5,019 posts

Posted 28 May 2014 - 01:27 PM

magonz,

 

Page 44 of the Fifth Ed. as attached.

 

 

Attached Files



#9 wenchop

wenchop

    Veteran Member

  • Members
  • 33 posts

Posted 28 May 2014 - 03:01 PM

As shown in your attachment, it goes as far to suggest to estimate the thermal expansion coefficient of the supercritical fluid, but to use this method you need to calculate a fire heat flow, and that is not clear how to do for a supercritical fluid, as there is no "wetted" area.

 

Also, page 43 of 6th edition gives an equation for relief load, but the assumption is ideal gas equations, and in my case the relief pressure is too high to apply ideal gas equations.

 

There is an alternative method in page 44, but it is rigorous, not good for preliminary calculation.   

 

And I still haven't found what I am looking for...



#10 Bobby Strain

Bobby Strain

    Gold Member

  • Members
  • 3,529 posts

Posted 28 May 2014 - 04:29 PM

Magonz,

     Your arrogance won't win friends. Or help, either.

 

Bobby



#11 breizh

breizh

    Gold Member

  • Admin
  • 6,724 posts

Posted 28 May 2014 - 11:38 PM   Best Answer

Magonz,

Consider this paper , you may find what you are looking for .

Don't expect too much from us , just a support .

Regards

Breizh


Edited by breizh, 29 May 2014 - 06:49 AM.


#12 fallah

fallah

    Gold Member

  • ChE Plus Subscriber
  • 5,019 posts

Posted 29 May 2014 - 02:02 AM

magonz,

 

My comments on your statements are in red color as follows:

 

As shown in your attachment, it goes as far to suggest to estimate the thermal expansion coefficient of the supercritical fluid, but to use this method you need to calculate a fire heat flow, and that is not clear how to do for a supercritical fluid, as there is no "wetted" area.

Yes, for supercritical fluid there isn't true latent heat, but you can treat the vessel containing such fluid as it is very high density gas filled because it makes sense. See also the statement from API 521 in the red box in attached.

Also, page 43 of 6th edition gives an equation for relief load, but the assumption is ideal gas equations, and in my case the relief pressure is too high to apply ideal gas equations.

Yes, the assumptions are based on ideal gas law and might not be valid for high pressure gases but it can be used for estimation as mentioned in API itself. If you wanted to use a PSV for only fire case without another credible scenario, no matter how much does the estimated relief load deviate from the real value but appears by using PRD you are trying to protect the vessel from failure in fire case. Then you can modify the calculated relief load , say, by using multiplyer of density ratio (critical density/maximum perfect gas density) and use as final relief load.

 

Attached Files



#13 wenchop

wenchop

    Veteran Member

  • Members
  • 33 posts

Posted 29 May 2014 - 06:59 AM

Magonz,

     Your arrogance won't win friends. Or help, either.

 

Bobby

 

Your condescension or patronizing attitude won't win friends.


Edited by magonz, 29 May 2014 - 07:01 AM.


#14 wenchop

wenchop

    Veteran Member

  • Members
  • 33 posts

Posted 29 May 2014 - 07:08 AM

Fallah:

 

Sounds very reasonable, but I cannot argue in front of peers that I used ideal gas equations at high pressures.

 

I also do not want to calculate a wetted area and expansion coefficient for a supercritical fluid. API 521: 

"Unwetted wall vessels are those that have no liquid in contact with the internal vessel walls (e.g. internal walls are
exposed only to a gas, vapor, or supercritical fluid or they are internally insulated regardless of the contained fluids). These include vessels that contain separate liquid and vapor phases under normal conditions but become single phase (above the critical) at relieving conditions."

 

 

What I will do is do the rigorous method, as there doesn't seem to be a simple approach.

 

But thank you anyway. 

 

Regards,


Edited by magonz, 02 June 2014 - 09:52 AM.