Conversion Of Psi/hr To M3/hr Of Air
Started by sn_sn, Jul 03 2014 06:50 AM
2 replies to this topic
Share this topic:
#1
Posted 03 July 2014 - 06:50 AM
Hi,
Is it possible to convert psi/hr pressure increase in vessel to Air Nm3/hr?
Actully at degassification membrane outlet we have installed one PSV set@190kPag.
so i was worried about PSV will leak under vacuum. so went back to vendor and vendor sent me test report of PSV.
it says..valve test started with vacuum between 13.37psi to 13.25psi. and valve had pressure increase rates of 0.053 psi/hr over the time of test.
so i want to convert this psi/hr to air Nm3/hr. because installed vacuum pump capacity is 150Nm3/hr(2 vac pump)..so if PSV leaks and pressurised the system we need higher capacity vacuum pump. PSV is 1" E orifice viton seated.
Is it possible to convert psi/hr pressure increase in vessel to Air Nm3/hr?
Actully at degassification membrane outlet we have installed one PSV set@190kPag.
so i was worried about PSV will leak under vacuum. so went back to vendor and vendor sent me test report of PSV.
it says..valve test started with vacuum between 13.37psi to 13.25psi. and valve had pressure increase rates of 0.053 psi/hr over the time of test.
so i want to convert this psi/hr to air Nm3/hr. because installed vacuum pump capacity is 150Nm3/hr(2 vac pump)..so if PSV leaks and pressurised the system we need higher capacity vacuum pump. PSV is 1" E orifice viton seated.
#2
Posted 03 July 2014 - 07:32 AM
You can. You need to know the volume of the space where the pressure declined in the vendors test stand. Then, use an EOS like the ideal gas law to calculate the number of moles of air that got in.
Edited by latexman, 11 July 2014 - 03:40 PM.
#3
Posted 11 July 2014 - 03:30 PM
Thanks...I did calculation by (p1v1/t1) n=(p2v2/t2)op..n normal condition..op means operating condition..
So ans I got 101.325×22.41/273=0.367×v2/298 so v2 is around 7.3 Nm3/hr...is it the correct method...??0.367kPa is 0.053 psi/hr pressure increase
So ans I got 101.325×22.41/273=0.367×v2/298 so v2 is around 7.3 Nm3/hr...is it the correct method...??0.367kPa is 0.053 psi/hr pressure increase
Edited by sn_sn, 11 July 2014 - 03:32 PM.
Similar Topics
Coefficient Of Conversion Of Electrical Energy Into Thermal Energy ForStarted by Guest_amx_* , 03 Apr 2024 |
|
![]() |
||
Conversion Of M3 Of Natural Gas To M3 Of LngStarted by Guest_sachico28_* , 30 Sep 2023 |
|
![]() |
||
![]() Calculation Tools: Unit Conversion, Drum, Compressor, Flare, Control VStarted by Guest_ReonArd_* , 16 Mar 2023 |
|
![]() |
||
Under What Conditions Can A Real Cstr Achieve A Higher Conversion ThanStarted by Guest_HWIK_* , 12 Dec 2022 |
|
![]() |
||
Define Conversion Reaction In Hysys Using VbaStarted by Guest_Ghirahim_* , 05 Jul 2022 |
|
![]() |