Dear All,
Please explain me the following'
1. Why weep hole is provided on PSV discharging to atmosphere?
2. What should be the size?1/2" or 6 mm?
3. On what basis the weep hole size should be selected?
Thanks in advance.
Pradip
|
Weep Hole Requirement
Started by kpa, May 09 2006 07:01 AM
2 replies to this topic
Share this topic:
#1
Posted 09 May 2006 - 07:01 AM
#2
Posted 09 May 2006 - 06:32 PM
if the relief is for vapor, then the tail pipe will be pointing straight up to keep the relieving flow away from anyone who may be in the area. Since it is pointing up, it can fill with rain water. So, the week hole is provided for drainage.
The 1/4" hole is more common to me.
The sizing basis is anything that will accomplish the job. 1/4" hole should do the job.
The 1/4" hole is more common to me.
The sizing basis is anything that will accomplish the job. 1/4" hole should do the job.
#3 Guest_kjthor_*
Posted 19 October 2008 - 02:21 PM
Don't forget the weep hole deflector so if the discharge ignites any jet flame from the weep hole won't impinge on the vessel or important piping and possibly cause overheating and failure. This was an oil & petrochemical underwriters' recommendation for many years and was eventually put into an industry code - API 2510 and 2510A for LPG facilities.
Similar Topics
Sil Rating Requirement For BurnersStarted by Guest_seuenergy_* , 13 Apr 2024 |
|
|
||
Compressed Air RequirementStarted by Guest_Mohamed cage_* , 14 Apr 2019 |
|
|
||
Requirement For Hydrogen (Pressurised) Gas Storage BlowdownStarted by Guest_panagiotis_e_* , 30 Nov 2023 |
|
|
||
Burners Flame Monitoring System RequirementStarted by Guest_Movers_* , 23 Nov 2023 |
|
|
||
Steam Requirement For Mea Reboiler - Co2 Capture From Flue GasesStarted by Guest_liquidcarbonic_* , 25 Sep 2023 |
|
|