Hi,
Is it necessary that all running piping/pipelines to be bonded together ?
or, is it the case that piping/pipeline with non-metallic gaskets in between the flanges shall only be bonded ?
Thanks in advance.
Regards.
|
Posted 07 January 2016 - 10:51 PM
Hi,
Is it necessary that all running piping/pipelines to be bonded together ?
or, is it the case that piping/pipeline with non-metallic gaskets in between the flanges shall only be bonded ?
Thanks in advance.
Regards.
Posted 07 January 2016 - 11:10 PM
hi ,
If flammable material , yes !
Breizh
Edited by breizh, 08 January 2016 - 05:17 AM.
Posted 08 January 2016 - 02:28 AM
Hi,
Even if metallic gasket is used at flange joints, for flammable material an external jump over strip at flange joints is recommended for electrical continuity.
Regards
K.Rajan
Posted 10 January 2016 - 02:56 PM
Hi,
If you are pumping a flammable material which is a known static accumulator such as Xylene. Earth Bonding between all flanged pipe work carrying the solvent is best practice and reduces probability of ignition.
However more important still is that the pumping velocity is kept below 1 m/s.
Regards,
Posted 11 January 2016 - 01:35 AM
To add to @siltonjm
Liquid velocity in the filling line shall be limited to 1m/s, until the filling line is submerged to avoid splashing and turbulence.
Posted 13 July 2016 - 01:07 AM
Is there any reference standards/codes stating requirement of electrical bonding?
Posted 13 July 2016 - 02:09 AM
Blesson.
You should consider google search engine , plenty of information are available.
Breizh
Posted 13 July 2016 - 05:57 AM
Sir,
Googled it & got some info.
NFPA 77
8.4 Flow in Pipe, Hose, and Tubing.
Here jumper wire is optional only. CAn we consider this as a general recommendation, for all services?
Posted 13 July 2016 - 09:07 PM
Hi ,
To me a jumper wire is a safe practice .
At my place we are dealing with flammable material and powder . All flanges are equipped with jumper .
hope this helps
Breizh
Earthing Dipsticks Of Underground Fuel TanksStarted by Guest_viiking_* , 16 Dec 2014 |
|
![]()
|
||
Earthing LugsStarted by Guest_kylene28_* , 18 Oct 2013 |
|
![]()
|
||
Ice - Expansion Due To Hydrogen BondingStarted by Guest_pyro38_* , 17 Dec 2008 |
|
![]()
|
||
EarthingStarted by Guest_mahesh lade_* , 28 Dec 2006 |
|
![]()
|
||
Earthing Of The Equipment With Nonconductive MocStarted by Guest_trilok_sontakke_* , 14 Sep 2005 |
|
![]()
|