Cooling Tower Design Question.
cooling tower design
14 replies to this topic
#1 norbert90
norbert90
Posted 11 January 2016 - 05:41 AM
I am trying to design an induced draft cooling tower that is able to cool 1000 m3/h from 33°C to 29°C at 26°C wet bulb T.
In order to calculate the required area for this tower, I need to choose a water loading factor (m3/h.m2); anyone have an idea how to get this number and based on what ?
Thanks in advance.
  • 6,912 posts
Posted 11 January 2016 - 11:48 AM   Best Answer
norbert90,
Let you consider the resources attached.
Hope this helps
#3 ADITYA.DUBEY
ADITYA.DUBEY
  • 32 posts
Posted 13 April 2016 - 11:34 PM
Dear all
I had asked a vendor to supply a cooling tower to cool the water supply of 20 m3/hr(5283 gallons/hr)  from 60 Deg C (140 F) to 35 Deg C(95 F) . Wet bulb temp is 28 Deg C(82.4 F).
According to my calculation total heat transfer requirement will be 165 Ton of Refrigeration(TR).
But vendor is supplying only 55 TR capacity cooling tower and saying it is sufficient for the purpose  and giving below justification.
Heat rejection rate = 500000 Kcal/hr = 165 TR
However a coefficient of Range-Approach =0.3 will be applied thus requirement = 55 TR.
I am unable to find any coefficient like that anywhere.
Range= 25 Deg C (45 F)
Approach = 32 Deg C (57.6 F)
Have anyone come across like such problem??
Aditya
#4 shantanuk100
shantanuk100
  • 104 posts
Posted 15 April 2016 - 12:18 AM
Dear Aditya,
Please post your calculation here too alongwith the final value.
Then we can compare the vendor's value and see where you or he might have been different.
Shantanu
#5 breizh
  • 6,912 posts
Posted 15 April 2016 - 01:02 AM
Hi aditya ,
Consider the resources attached to support your work.
Hope this helps
56200358
  • 18 posts
Posted 27 June 2016 - 12:03 PM
Hello
how can i select the type of cooling tower make up? RO or pretreatment water or raw water(river-sea water)? what type of water is usually used?
(I know fundamentals of cooling tower such as COC,....)
#7 breizh
  • 6,912 posts
Posted 27 June 2016 - 09:07 PM
The type of the water is defined based on  metallurgy of the equipment , the availability and the treatment in place . I would advise you to contact a reputable vendor of chemical treatment for cooling water .This guy will perform tests on different samples provided . Economics should be the driver ( water consumption (blow down) / chemical cost/ equipment ,,,,)
Hope this helps
#8 Chemical.Engineer
Chemical.Engineer
  • 12 posts
Posted 08 August 2016 - 12:56 AM
Hello
i want to redesign cooling system for a existing wet cooling tower with less flow than before.
1- for available cooling tower(the cooling tower has been constructed), how can i calculate L/G?
2- if i want to simulate a dry cooling tower, what are the minimum and optimum approach in dry cooling tower?
#9 breizh
  • 6,912 posts
Posted 08 August 2016 - 01:13 AM
For point 1 , the only thing you need to consider is to work on the electrical power consumption , using a VSD for the fan(s) . For the pumps , probably better to redesign .
Make sure that the water distribution is correct in the cooling tower to prevent scale formation and packing to collapse .
For L/G  calculation take a look at post #2
For point 2 , define your requirement and discuss with the vendor .
my view.
Edited by breizh, 08 August 2016 - 01:26 AM.
#10 56200358
56200358
  • 18 posts
Posted 18 October 2016 - 04:12 AM
Hello
i want know minimum velocity for line sizing in cooling towers loop. Shall we consider velocity critria for cooling water or suction and pump discharge?if we shall use cooling water critria, how much shall we consider?i have seen minimum velocity 1 m/s also 8 ft/s in another reference for cooling waters.which one is true(please introduce reference)?soft water is used for this loop.
#11 breizh
  • 6,912 posts
Posted 18 October 2016 - 10:36 PM
Let you try your best Friend Google or other engine , key words : Cooling water pipe velocity .
#12 Johns923
Johns923
Posted 21 September 2017 - 10:07 AM
Breizh,
the links in your file titled "Cooling Tower Thermal Design" do not work. Do you by any chance happen to have an updated link to the associated examples?
Thank you!
John
#13 breizh
  • 6,912 posts
Posted 21 September 2017 - 10:14 AM
Hi John,
Just a PDF !
let you try Google or your favorite engine .
Edited by breizh, 21 September 2017 - 11:26 AM.
#14 Takechi
Takechi
  • 43 posts
Posted 28 September 2017 - 11:48 PM
Dear Breizh or every one
Could you please share spreadsheet in Cooling tower thermal design.pdf to me.
I try to download these spreadsheet but I cannot.
Salapao
#15 breizh
  • 6,912 posts
Posted 29 September 2017 - 05:35 AM
Good day all ,
I cannot offer better and you need to perform calculation using the examples attached .
another good resource with software is : APPLIED INDUSTRIAL ENERGY AND ENVIRONMENTAL MANAGEMENT from Z.K Morvay
Edited by breizh, 30 September 2017 - 06:18 AM.