Dear all
I had asked a vendor to supply a cooling tower to cool the water supply of 20 m3/hr(5283 gallons/hr) from 60 Deg C (140 F) to 35 Deg C(95 F) . Wet bulb temp is 28 Deg C(82.4 F).
According to my calculation total heat transfer requirement will be 165 Ton of Refrigeration(TR).
But vendor is supplying only 55 TR capacity cooling tower and saying it is sufficient for the purpose and giving below justification.
Heat rejection rate = 500000 Kcal/hr = 165 TR
However a coefficient of Range-Approach =0.3 will be applied thus requirement = 55 TR.
I am unable to find any coefficient like that anywhere.
Range= 25 Deg C (45 F)
Approach = 32 Deg C (57.6 F)
Have anyone come across like such problem??
Thanks
Aditya