I looked over your schematic and am not sure what valves will and will not have automated actuators. Though I am certainly NOT a compressor expert, I have seen installations where the anti-surge valve is inside the suction and discharge isolation valves. In you case, for example, you might have a fail closed inlet isolation valve, then tie in your anti-surge (spill-back) line, then go through your air cooler, your trim cooler and into your compressor. On the discharge side, you'd come out of the compressor, split off for the spillback line, and then have your fail closed discharge isolation valve. The anti surge valve would fail open.
Though I would prefer an arrangement as described above, it does have the disadvantage of increasing the gas volume trapped between your isolation valves. Only by examining your actual piping layout or design can you tell how significant that aspect of the design compares to the positive aspects.
Good luck in your design,
Doug
I would do this. As Doug says the voulme trapped between auto shutdown valve increases, so you have to evaluate if the compressor will not surge when the spill back lines opens. I believe the maximum time for spillback loop to react is of the order of 500ms, which is a function of opening time of the anti-surge valve, and the volume trapeed between valves.
Regards