Spool Installation Upstream Of Psvs
#1
Posted 18 May 2018 - 09:36 AM
why is a spool installed upstream of PSVs flange to flange of the relevant vessel
#2
Posted 18 May 2018 - 10:20 AM
Hi Ahmadi,
That pipe spool actually is to be installed there as a "positive isolation" facility; hence, in maintenance cases this spool will be removed and the vessel flange will be blinded. Then, as the blind has to be removed before spool re-installation, there would be no safety issue due to forgetting to change the spectacle blind status from close to open by operator in the case without a spool installation.
#3
Posted 18 May 2018 - 11:24 AM
thank you for your attention to my questionquestion and your comprehensive answer.
In conclusion,using an end blind flange instead of spectacle blind is the reason, isn't it?
#4
Posted 18 May 2018 - 12:08 PM
Hi Ahmadi,
The spool will be equipped with a flange at both ends and would be installed inline between the PSV and related vessel. Then, for creating isolation during maintenance, there would be no need for a spectacle blind and it's adequate to remove the spool and isolate the vessel with a blind.
#5
Posted 18 May 2018 - 12:24 PM
I am dealing with a spool equipped vessel, there's a spacer upstream of the spool between the vessel and psv.
anyway, thanks a lot.
Edited by R.Ahmadi, 18 May 2018 - 12:27 PM.
#6
Posted 18 May 2018 - 12:33 PM
Hi,
If there is a both ends flaged spool between the PSV and relevant vessel there is no need to having any spacer upstream/downstream of the spool...
#7
Posted 18 May 2018 - 12:41 PM
great,
what's the meaning of positive isolation precisely?
#8
Posted 18 May 2018 - 12:52 PM
Hi,
Positive isolation is simply a type of isolation in which no leakage is tolerated. Then isolation with a valve isn't a positive isolation and isolation with a blind either by inserting it between two inline flanges or after removing a pipe spool is considered as a positive isolation.
#9
Posted 22 May 2018 - 06:56 AM
Hi
Please there are any docs talk about isolation process and positive in design phase?
#10
Posted 22 May 2018 - 05:46 PM
Hi ,
you may find some interest reading the document attached.
Breizh
Similar Topics
![]() Psvs Relieving To Closed Drain SystemStarted by Guest__1angelia23_* , 12 Jan 2025 |
|
![]() |
||
Requirement Of Buffer Vessel Upstream On Reciprocating Compressor.Started by Guest_ErDhrj05_* , 16 May 2024 |
|
![]() |
||
Buffer Tank Sizing Upstream Screw CompressorStarted by Guest_Process_1601_* , 09 May 2024 |
|
![]() |
||
Two Psvs Have More Or Less Same Set PointsStarted by Guest_johneyissac98_* , 16 Jan 2024 |
|
![]() |
||
![]() ![]() Multiple Psvs Relief RateStarted by Guest_fmalik_* , 02 Dec 2023 |
|
![]() |