#1
Posted 02 December 2023 - 12:11 PM
When adding multiple psvs to a vessel (fire case) is the total relief rate just divided by 2 in case the two psvs (same type) are added. API doesn't explicitly mention this therefore I wanted to confirm.
Regards,
#2
Posted 02 December 2023 - 12:18 PM Best Answer
Some companies put a second PSV as an inline spare. In this case, each PSV’s capacity must be >= the total relief rate.
#3
Posted 03 December 2023 - 06:36 AM
When adding multiple psvs to a vessel (fire case) is the total relief rate just divided by 2 in case the two psvs (same type) are added. API doesn't explicitly mention this therefore I wanted to confirm.
Hi,
When sizing for multiple valve applications, the total required area is calculated based on an overpressure of 16% or 4 psi, whichever is greater (for fire case 21%). Then two PSVs with the same size would be selected to cover the calculated total required area. Hence the relief loads of such two PSVs might or might not be equal.
Edited by fallah, 03 December 2023 - 07:37 AM.
#4
Posted 03 December 2023 - 07:06 AM
#5
Posted 04 December 2023 - 12:02 AM
When adding multiple psvs to a vessel (fire case) is the total relief rate just divided by 2 in case the two psvs (same type) are added.
API allows 1st PSV 80 cfps capacity, 2nd PSV 20 cfps capacity while firecase relief is 90 cfps.
#6
Posted 04 December 2023 - 07:09 AM
API allows 1st PSV 80 cfps capacity, 2nd PSV 20 cfps capacity while firecase relief is 90 cfps.
cfps? API # and section, please?
#7
Posted 04 December 2023 - 07:18 AM
When adding multiple psvs to a vessel (fire case) is the total relief rate just divided by 2 in case the two psvs (same type) are added. API doesn't explicitly mention this therefore I wanted to confirm.
API 520 Part 1 says:
Capture 1.JPG 29.35KB 2 downloads
Capture 2.JPG 64.04KB 1 downloads
#8
Posted 05 December 2023 - 12:25 AM
Hi,
To add to the discussion, consider the documents from Lesser and from Crosby (with examples)
Breizh
Attached Files
#9
Posted 11 December 2023 - 11:56 PM
Sorry for delay, I have been away from computer for a week.
API allows 1st PSV 80 cfps capacity, 2nd PSV 20 cfps capacity while firecase relief is 90 cfps.
cfps?
cfps = cubic feet per second
API allows 1st PSV 80 cfps capacity, 2nd PSV 20 cfps capacity while firecase relief is 90 cfps.
API # and section, please?
This is a reference to the statement you provided before
Each does not have to be exactly half. But yes, the sum of the 2 PSV’s capacities must be >= the total relief rate.
#10
Posted 12 December 2023 - 06:18 AM
Similar Topics
Ammonia Evaporation Rate InquiryStarted by Guest_aslungaard_* , 30 Mar 2024 |
|
|
||
Duplication Of Psv And Flow Rate For Exchanger Tube Rupture ScenarioStarted by Guest_Platonicus_* , 11 Mar 2024 |
|
|
||
Psv Fire Case Relief Load CalculationStarted by Guest_mahmooddalvi09_* , 21 Feb 2024 |
|
|
||
Two Psvs Have More Or Less Same Set PointsStarted by Guest_johneyissac98_* , 16 Jan 2024 |
|
|
||
Multiple Effect Evaporator Calculation With Multiple ComponentsStarted by Guest_addiesalsabil_* , 13 Jan 2024 |
|
|