Tank Jacket Control Valve
#1
Posted 15 June 2018 - 08:31 AM
This why we can directly control the area of the heat transfer.
Is it recommended?
#2
Posted 15 June 2018 - 11:05 AM
Both has pros and cons:
The valve in the condensate line provides more control at low capacity. It is slow, specially when reducing the load, since to modify the area you have to wait until condensates cover that area,
The valve at the inlet is fast, but when the condensation pressure goes below that of the condensate return line, it starts to behave erratically, since it accumulates condensate, area is reduced, pressure rise, condensate is pumped out, etc, etc, etc,. it can be solved with a pumping steam trap, but those are relatively expensive compared with normal traps.
#3
Posted 15 June 2018 - 01:55 PM
#4
Posted 16 June 2018 - 07:05 AM
See this reference describing best practice to control tank jackets:
http://www.spiraxsar...nd-jackets.aspx
#5
Posted 27 June 2018 - 04:07 AM
Does anyone have experience with condensate control?
Do I need a steam trap before or after the valve?