I have been going through the various details related to PSV chattering due to exceeding the inlet pressure loss criteria for vapor services in comparison to the PSV blowdown set by the manufacturer.
However, I was recently discussing with another Engineer the statement in API 520 PII- section 7.3.4 : that keeping the pressure loss below 3% becomes progressively difficult for low pressure and / or as the orifice PRV increase'' . I believed that this difficulty in meeting the criteria for such scenarios are related to low relieving pressure mandating larger PSV area (as calculated by API 520 PIi.e. effective area). Accordingly, the rate area would also be large leading to fast pressure drop as soon as the PSV opens specially when the operating pressure is low and is not widely different from the PSV set point. However, the Engineer disagreed with any relation between the difficulty of meeting the 3 % and the size of the PSV or the fact of low pressure applications. I need your views on this.
Additionally, I was reading several opinions that in case 3% inlet pressure loss can't be met, one of the solutions is either to use a pilot operated valve with remote sensing, increase the blowdown of the PSV if possible OR install staggered PSVs. I was challenged by the same engineer that staggering smaller PSVs will not help in resolving the issue of exceeding the 3% stating that eventually both PSVs will have their inlet lines experiencing the same flow. I am aware that symmetrical piping also should play a role in resolving the issue, YET the Engineer insists that having a staggered installation of PSVs has no solution with regards to the inlet pressure loss. I also appreciate your views on this.
Thanks alot