HI there,
I want to calculate time required for venting all hydrogen gas from hydrogenator which is operated under 4Kg/cm2 through 40 mm vent.
I tried through torricelli equation but result found abnormal.
|
Posted 07 June 2019 - 01:46 AM
HI there,
I want to calculate time required for venting all hydrogen gas from hydrogenator which is operated under 4Kg/cm2 through 40 mm vent.
I tried through torricelli equation but result found abnormal.
Posted 07 June 2019 - 02:50 AM
hi ,
Please consider reading this document to support your work .
Monitoring the effectiveness of the process is key .
good luck
Breizh
Edited by breizh, 07 June 2019 - 08:36 AM.
Posted 07 June 2019 - 07:58 AM
Torriceli is for liquids.
Is there a restriction orifice? Use choked flow.