Hi guys
Can anyone explain me what are the risk in a fired heater (fired with gas) when the pilot gas has an high- high pressure or a low-low inlet pressure , or when the fuel gas has a low low or an high high inlet pressure
Best regards
Fired Heater
Started by pasquale, Oct 05 2006 02:48 AM
Posted 05 October 2006 - 02:48 AM
Posted 05 October 2006 - 06:54 AM
Well, basically the PSHH and PSLL are there to prevent loosing the flame. When a (pilot) burner has been lit and fuel gas pressure remains within the required pressure range (as per burner curve), you can safely assume that there will indeed be a flame. The PSHH/PSLL combined with flame detection (e.g. thermocouple for pilot flame and UV detection for main burners) ensure that there is a flame.
When you loose the flame and heater is not tripped, an explosive atmosphere can build-up in the heater box. If this is subsequently ignited this results in an explosion damaging the heater (and maybe hurting people).
Posted 05 October 2006 - 07:51 AM
Thanks for the reply basically I knew that there is the possibility of loss of flame but I don't understand why it happens.
So, you can explain me ?
Moreover what are the burner curve ?
Best regards
Best regards
Posted 05 October 2006 - 09:27 AM
Burner curve of a particular burner is a curve showing amount of heat released vs. burner fuel pressure. It should be provided by the heater supplier (who should obtain it from the burner supplier).
If fuel pressure is too high the air/fuel mixture at the burner would become too rich (flame is "blown off"), while if fuel pressure is too low the air/fuel mixture would become too low. Both cases result in loss of flame.
Posted 05 October 2006 - 09:54 AM
Thanks gvdlans
Basically if i have a high fuel gas pressure at the burner the gas flowrate is too high and i have a air/gas mixture less than the correct molar or weight ratio.
on the contrary for fuel gas low pressure.
It's correct?
Best regard
It's correct?
Best regard
Posted 05 October 2006 - 01:17 PM
Correct, and the heater/burner vendor can tell you in what pressure range the burner can operate safely.
![]() Fired Heaters/ Burners/ Flue VelocityStarted by Guest_Lyne_* , 15 Mar 2024 |
Selection Type Of Heater For Refrigerated PropaneStarted by Guest_livetolove003_* , 07 May 2025 |
Electric Heater In Regeneration Absorption BatteryStarted by Guest_alaasleem2026_* , 01 Sep 2024 |
![]() Cross Temperature In Heater Exchanger (Lng)Started by Guest_Yogan_* , 21 Feb 2024 |
Why To Maintain The Skin Temperature At 150Degc In Fired Heater ?Started by Guest_johneyissac98_* , 12 Jan 2023 |