Muilti purpose storage tank (for acetone, MEK, acetonitril,etc.) , filling from the top, in order to avoid static eletricity, we should apply a dip pipe or a J angle pipe?
|
|
Posted 23 February 2020 - 06:51 AM
Muilti purpose storage tank (for acetone, MEK, acetonitril,etc.) , filling from the top, in order to avoid static eletricity, we should apply a dip pipe or a J angle pipe?
Posted 24 February 2020 - 10:42 AM
Hi,
Your intention should be to avoid free fall of hydrocarbon at high velocities in the tank which is the reason for static electricity generation.
Hope this clarifies your doubt.
Posted 29 February 2020 - 07:28 AM
Hi,
a dip pipe with hole in upper part to prevent siphoning .
http://www.processop...e/FE_Chp07d.htm
https://www.eng-tips...d.cfm?qid=91957
Good luck,
Breizh
Edited by breizh, 02 March 2020 - 06:35 AM.