Pressure Control Of A Separator

pressure control separator pressure control valve opening control

4 replies to this topic
Share this topic:
| More

#1 james.corrobro@gmail.com

james.corrobro@gmail.com

    Veteran Member

  • Members
  • 35 posts

Posted 07 May 2021 - 07:33 PM

There is a separator with two control valves to maintain pressure of the equipment (separator).
 

The purpose is to maintain 250 psig at separator. For the pressure control valve-1, at what pressure should it start to open ? will it be at 250 psig or higher. What sizing cases should be made for PV-1? Should it be 250 psig at inlet? What will be controller output % at 250 psig pressure?
 

Also for pressure control valve-2 what pressure should it start to open? What sizing cases should be made for PV-2?

 

Attached File  pressure control.jpg   56.19KB   1 downloads



#2 breizh

breizh

    Gold Member

  • Admin
  • 5,118 posts

Posted 07 May 2021 - 10:47 PM

Hi ,

Common sense should prevail!

The controller will do the job , set point  is yours .

Good luck .

Breizh



#3 fallah

fallah

    Gold Member

  • ChE Plus Subscriber
  • 4,789 posts

Posted 08 May 2021 - 12:34 AM

There is a separator with two control valves to maintain pressure of the equipment (separator).
 

The purpose is to maintain 250 psig at separator. For the pressure control valve-1, at what pressure should it start to open ?250 psig will it be at 250 psig or higher. What sizing cases should be made for PV-1? Should it be 250 psig at inlet? Yes What will be controller output % at 250 psig pressure? Normally 50%
 

Also for pressure control valve-2 what pressure should it start to open?250 psig and the controller output goes beyond 50% What sizing cases should be made for PV-2?same flow rate as the valve-1 and pressure drop according to the flare pressure

 

attachicon.gif pressure control.jpg



#4 james.corrobro@gmail.com

james.corrobro@gmail.com

    Veteran Member

  • Members
  • 35 posts

Posted 08 May 2021 - 01:37 AM

fallah- thanks,
what is meant by controller output %
like what is meant by 50% of controller output?
when controller output goes beyond 50%...does it mean pressure is rising much high than 250 psi

 

There is a separator with two control valves to maintain pressure of the equipment (separator).
 

The purpose is to maintain 250 psig at separator. For the pressure control valve-1, at what pressure should it start to open ?250 psig will it be at 250 psig or higher. What sizing cases should be made for PV-1? Should it be 250 psig at inlet? Yes What will be controller output % at 250 psig pressure? Normally 50%
 

Also for pressure control valve-2 what pressure should it start to open?250 psig and the controller output goes beyond 50% What sizing cases should be made for PV-2?same flow rate as the valve-1 and pressure drop according to the flare pressure

 

attachicon.gif pressure control.jpg

 



#5 fallah

fallah

    Gold Member

  • ChE Plus Subscriber
  • 4,789 posts

Posted 08 May 2021 - 01:43 AM

 

what is meant by controller output % In split range control system the controller output splits into 0-50% and 50-100% to manipulate relevant actuator.
like what is meant by 50% of controller output?
when controller output goes beyond 50%...does it mean pressure is rising much high than 250 psi it means the pressure will tend to rise higher than 250 psig

 

 

 

 