Hello,
This is with reference to latest edition of API-2000 (7th edition), as a user I have a query on basis of inbreathing calculation to be used for tank. As covered in API2000 section 3.3.2.3.2, the thermal inbreathing of a tank is function of tank volume and latitude at which tank is located. The basis of the equation VIT = C *Vtk 0.7 * Ri is detailed out in Annexure G.3.
As per Annexure G.3, the equation for general method has been worked out based on following assumptions :
- Tank sizes : Any sizes
- Initial Temperature : 55 deg C
- Rainwater Temperature : 15 degC
- Free Convection in tank : 4 W/m2K
- Maximum rate of temperature : Calculated – Considering worst case rain intensity of 225 kg/m2h
Experiment was conducted based on above conditions and the equation in section 3.3.2.3.2 is derived based on above worst boundary limits. However, as per Figure G.4, it provides rate of temperature change for a given tank with respect to different rain intensity.
Query/Proposal for section 3.3.2.3.2 modification :
As per API2000 section 3.3.2.3.2, the thermal inbreathing is calculated based on worst case rain intensity of 225 kg/m2h. However, the thermal inbreathing rate needs to be calculated based on worst rain intensity experienced for the specific geographical location. The Figure G.4 to be used for determine the maximum rate of temperature with respect to tank volume and rain intensity. The same rate of temperature to be used to calculate the additional moles of air required when the tank vapor space contracts from initial temperature of 55 degC to final temperature determined based on Figure G.3 (considering maximum rate of temperature).
Above exercise will provide actual thermal inbreathing flow rate to be considered for tank with respect to rain intensity of that particular geographical location. E.g. tank located in Sahara desert and in Thailand with same dimensions will have different thermal inbreathing requirements whereas as per API2000 sction 3.3.2.3.2 this is function of tank volume and latitude only (tank on same latitude may have different rain intensity).
Suggestion :
The user should be allowed to use Fig G.4 for performing thermal inbreathing requirement instead of calculating it based on API2000 section 3.3.2.3.2, since this will also take rain intensity into consideration which is presently calculated based on default rain intensity of 225 kg/m2h.
Appreciate feedback from experts here!
Regards
AJ