Hello everyone,
I would like to ask you what procedure we follow in order to find out the most credible overpressure scenario for sizing a PSV?
Thank you in advance!
|
Posted 13 December 2021 - 06:31 AM
Hello everyone,
I would like to ask you what procedure we follow in order to find out the most credible overpressure scenario for sizing a PSV?
Thank you in advance!
Posted 13 December 2021 - 06:56 AM
I would like to ask you what procedure we follow in order to find out the most credible overpressure scenario for sizing a PSV?
Hi,
In general, refer to API 521...
Posted 13 December 2021 - 07:04 AM
Hi,
To add to Naser's reply a few documents.
Breizh
Posted 13 December 2021 - 07:35 AM
Determine ALL credible scenarios, calculate relief area for each (take care to use the correct phase flow coefficient). the largest relief area is worst case.