Isenthalpic Throttling With Flashing Liquid
16 replies to this topic
#1 lofarcio
lofarcio
  • 4 posts
Posted 06 May 2022 - 03:38 AM
I don't understand why the flow through the throttling valve in cooling cycles is assumed isenthalpic.
The usual justification is that since no moving parts nor heat transfer, then total energy must be constant, and since kinetic energy is similar for similar input-output cross-sectional areas, enthalpy is approximately the same.
But this is only valid for liquids (constant density), and this is not the case in cooling cycles. Since the liquid is close to saturation, it flashes when throttled, and then density falls greatly with the formation of vapor. Then, by continuity, average speed increases also greatly for equal areas.
With sample calculations for R134a between 9 and 2 bars absolute, it can be seen that density falls from ca. 1000 kg/m3 for HP saturated liquid to 36 kg/m3 for 26.7 % LP vapor quality. Then, average speed increases from 1 to 33 m/s, and 32 m/s squared divided by two is 512 J/kg, much more than the latent enthalpy of evaporation.
Under these conditions, how is it that the difference in kinetic energies can be assumed to be negligible?
Sorry if the question has been posted already somewhere or my analysis have great mistakes; I've been unable to find an answer. Any help will be highly appreciated.
#2 latexman
  • 1,923 posts
Posted 06 May 2022 - 09:00 AM
Kinetic energy is not neglected.
Even for the simple case of idea gas flow, we can observe that: Pin > Pout, velin < velout (where P = pressure and vel = velocity). These observations confirm the theory that hin = hout. Remember h = u + Pv (v = specific volume), so if pressure decreases then specific volume must increase if enthalpy is to remain constant (assuming u is constant).
Ditto for more complex two-phase flow.
#3 lofarcio
lofarcio
  • 4 posts
Posted 07 May 2022 - 12:10 PM
Many thanks for answering, Sir. However, I think your explanation doesn't address my question. You assume enthalpy "is to remain constant", and I am questioning why it must be so from first principles.
If you assume enthalpy is the same input-output, you are assuming kinetic energy difference is negligible. This is so because conservation of total energy says that the difference in enthalpy plus kinetic energy is equal to heat plus (or minus) mechanical work on moving parts. Throttling valves have no moving parts and are usually assumed adiabatic due to their small size. Then, difference of total energy must be zero, and the only way the difference of enthalpy be zero is that also that of kinetic energy be zero.
#4 latexman
  • 1,923 posts
Posted 07 May 2022 - 06:12 PM
Oh, yes.  I blew it, didn't I.  The problem is not with the definition of enthalpy, it is with the usual simplification of the steady flow energy equation for a throttling process/valve:
H1 + mV12/2 + mgZ1 + Q - W = H2 + mV22/2 + mgZ2
Adiabatic, no work, and negligible kinetic and potential energy yields the usual simplified throttling equation:
H1 = H2
One just has to derive a working equation that is useful for you:
H1 + mV12/2 = H2 + mV22/2
#5 lofarcio
lofarcio
  • 4 posts
Posted 07 May 2022 - 07:38 PM
H1 = H2
Thanks again, Sir. I will rephrase my question.
With a liquid, density is constant, so that velocity and kinetic energy are constants too, due to continuity (for a constant cross-section). Then, from the first principle of thermodynamics in an adiabatic flow passage (q = 0, w = 0, so that h + v2/2 = const.), it follows that enthalpy is also a constant.
But in the throttling valve of a refrigeration cycle, the liquid flashes and thus average density decreases greatly, so that continuity tell us that average velocity increases greatly too.
Then my question is:
What is the basis to assume that the variation of average kinetic energy is still negligible, which is the only way to assume that enthalpy continues to be a constant?
Thank you again for your answers.
#6 breizh
  • 7,035 posts
Posted 08 May 2022 - 02:11 AM
Consider this resource to support your work:
https://www.controlg...ashco_Fluid.pdf
#7 latexman
  • 1,923 posts
Posted 08 May 2022 - 06:24 AM
H = U + PV
U = internal energy.
PV = the work required to establish the system's physical dimensions, i.e. to make room for it by displacing its surroundings.
In the definition of enthalpy, there is no movement.  It is simple the energy, relative to a reference state, for a substance to exist in it's surroundings.  Therefore, there is no basis that I can see to consider kinetic energy terms in the enthalpy or enthalpy derivation.
There is a basis to consider kinetic energy terms in the steady flow energy equation.
#8 lofarcio
lofarcio
  • 4 posts
Posted 08 May 2022 - 06:26 AM
Thank you very much, Sir.
#9 Abdellahi
Abdellahi
  • 5 posts
Posted 22 May 2024 - 07:08 AM
Hi breizh and lofarcio,
The link doesn't work for me. Does it still work for you?
#10 breizh
  • 7,035 posts
Posted 22 May 2024 - 07:41 AM
Not working !
#11 latexman
  • 1,923 posts
Posted 22 May 2024 - 07:45 AM
Is this it?  https://www.studocu....-valves/8178647
#12 Abdellahi
Abdellahi
  • 5 posts
Posted 22 May 2024 - 08:11 AM
Hi Latexman it's works!!!! great
Do you all understand why kinetic energy is neglected? the book doesn't explain it.
Why from H1 + mV12/2 + mgZ1 + Q - W = H2 + mV22/2 + mgZ2
We have H1=H2. I undestand why we can assume the potential energy the same due to valve geometry.
But why the velocity is the same(or kinetic energy neglected)
The velocity is normally higher due to that throttling (venturi effect)
#13 latexman
  • 1,923 posts
Posted 22 May 2024 - 08:24 AM
On what page?
#14 Abdellahi
Abdellahi
  • 5 posts
Posted 22 May 2024 - 08:38 AM
From the first thermodynamic low, we have :
H1 + mV12/2 + mgZ1 + Q - W = H2 + mV22/2 + mgZ1  (1)
and throttling porcess is considered isenthalpic, so :
H1=H2 (2)
I try to understand, how from equation (1)  we obtain equation (2)
-We can considerer Q and W =0
- We can considerer that Z1=Z2  for a valve due to its geometry
so the equation ( 1)  is now:
H1 + mV12/2=H2 + mV22/2 (3)
So how from eq (3)  we get  H1=H2 without considering V1=V2
But can we considerer that since throttling higher the velocity
#15 latexman
  • 1,923 posts
Posted 22 May 2024 - 09:14 AM
Take a look at the section titled "Proof that the specific enthalpy remains constant" on Wikipedia.  Their derivation started with different equation/basis as yours.  It also depends on where State 1 and State 2 are, right?  The two States are usually at the upstream and downstream flange of the valve.  The pinch point in the valve is not usually one of the States.
#16 EnggExp
EnggExp
  • 10 posts
Posted 17 July 2025 - 05:33 AM
even with large density drops, the increase in kinetic energy is still small (<< 1%) compared to the enthalpy changes, so the isenthalpic assumption is valid for design-level analysis.
#17 twell
twell
  • 31 posts
Posted 20 July 2025 - 03:40 AM
you can solve a constant energy flash, see for example
https://www.cheresou...lashing-liquid/
Edited by twell, 20 July 2025 - 03:45 AM.