Closed Cooling Water System Balancing Valve Preferred Location ?
Posted 14 July 2022 - 01:18 PM
I am considering to locate the balancing valve on the supply as I intend to make the isolation valve on the return as locked open to provide an open path to a PSV on the expansion drum for a relief scenario.
Posted 14 July 2022 - 02:33 PM
A relief valve on each exchanger is probably less costly than a lock open valve. And you won't have to monitor the valve. It sounds as if this is a small system. Otherwise you would use direct air intercoolers.
Posted 14 July 2022 - 03:08 PM
Just curious why would a PSV be less expensive than LO valve?
I do not want to digress this topic towards overpressure protection but if we set aside LO valve and point to main query look, is there a preferred location of the manual balancing valve? These should be just set once during commissioning and start-up based on the design flow.
Posted 14 July 2022 - 03:56 PM
What you are going to find for a tube rupture case is a tremendous relief rate. Because all the liquid must accelerate the required pressure will be much greater than 11 bar. It's unlikely that 11 bar is high enough in this instance. If this is a small system, a double pipe exchanger will eliminate the need for overpressure protection resulting from a tube rupture.
Edited by Bobby Strain, 14 July 2022 - 04:39 PM.
Posted 14 July 2022 - 05:10 PM
Anyone, any feedback on the balancing valve location before this thread becomes an overpressure protection focused and I am being told off for not putting this query in the correct forum? ????
Posted 14 July 2022 - 06:42 PM
You need to hire a professional who can conduct a dynamic analysis. The results may show that you need a rupture disk on the heat exchanger. The usual steady state analysis is not sufficient.
Psv For Refrigeration SystemStarted by Guest_runnerup_* , 30 Jun 2025 |
![]() Guidance On Sizing Jacketed Pipe For Glycerine CoolingStarted by Guest_Kentucky08_* , 28 Jun 2025 |
![]() Recommended Installation Location For "pressure High" InterlocStarted by Guest_omupei_* , 20 Jun 2025 |