Switch Vs Transmitter
#1
Posted 29 July 2022 - 12:57 PM
This is a kind of continuation of my previous post.
I would like to ask you two questions:
What are the differences between switch and transmitter? (For example temperature switch and temperature transmitter)
When we prefer to use switch and when we prefer to use transmitter?
Thank you in advance!
#2
Posted 29 July 2022 - 01:52 PM
Some kitchen analogies...
A common kitchen appliance is an electric kettle to boil water. These do not usually reveal the temperature of the water as it heats up. Instead, it contains a temperature switch that is activated at a preset level which cuts the power to the device after a roiling boil begins. In this case, the switch is entirely adequate for it purpose.
The electric oven in my kitchen has a digital readout which continually displays the measured temperature inside the oven. The oven temperature measurement is transmitted to the computer controller built into the oven which adjusts the heating elements to try to maintain the setpoint that the cook enters. For this service, a temperature switch would not be adequate.
#3
Posted 29 July 2022 - 05:10 PM
Switch is link with a proteccion device to the process
Transmitter is an indication of the process variables
Horacio
#4
Posted 30 July 2022 - 03:59 PM
#5
Posted 30 July 2022 - 03:59 PM
#6
Posted 31 July 2022 - 12:49 PM
What are the differences between switch and transmitter? (For example temperature switch and temperature transmitter)
When we prefer to use switch and when we prefer to use transmitter?
Hi,
A Switch is normally to be applied to keep a process variable, say level, within a predefined range hence just needs to be set at mentioned range boundaries by linking to a pump keeping from running dry at below of lower range boundary and to avoid suction drum overflow at top of higher range boundary. It's obvious, no measuring is required and the switch acts intermittently when the process variable reaches to the range boundaries.
A transmitter, on the other hand, is normally to be applied to keep a process variable, say level, at a predefined value hence continuously measures a process variable over a range of values to feed a controller for modulating a level control valve (or for running a pump with variable speed drive) to keep the mentioned preset process variable (here level) as constant as possible.
#7
Posted 31 July 2022 - 11:07 PM
Hi,
Often switches are called Dry contacts , this means they can be only in 2 positions 1or 0 over the time ,very useful to start and stop an equipment .
By comparison a transmitter delivers a continuous signal over the time , could be 4-20 mA or 0-10 Volt ,for process monitoring.
Breizh
#8
Posted 04 August 2022 - 01:22 AM
Similar Topics
![]() Flow Switch High RangeStarted by Guest_Lyne_* , 11 Apr 2024 |
|
![]() |
||
![]() Flow Element / Orifice With 2 Transmitter SignalStarted by Guest_nguyenmd147_* , 01 Dec 2023 |
|
![]() |
||
How To Switch 2 Aspen Hysys Simulations When Connected To ExcelStarted by Guest_nfbeusebio_* , 14 Nov 2023 |
|
![]() |
||
Limit Switch/position SwitchStarted by Guest_panoska_* , 25 Jul 2022 |
|
![]() |
||
Level SwitchStarted by Guest_TheChemEng_* , 17 Jan 2020 |
|
![]() |