Recently I had come across a facility having ESDV(Emergency shutdown valve) with 2 step closure to avoid water hammer effect. Is it allowable ESDV to have 2 step closure arrangement?
regards
stu
|
Posted 27 November 2024 - 09:12 AM
hi all,
Recently I had come across a facility having ESDV(Emergency shutdown valve) with 2 step closure to avoid water hammer effect. Is it allowable ESDV to have 2 step closure arrangement?
regards
stu
Posted 27 November 2024 - 12:07 PM
Recently I had come across a facility having ESDV (Emergency shutdown valve) with 2 step closure to avoid water hammer effect. Is it allowable ESDV to have 2 step closure arrangement?
Hi,
In the ESDV you mentioned "Slow Continuous Closing" has been substituted by "Two Steps Closure".
I think the important factor is the total time of closure. If the two steps closure takes a time almost equal to that of the continuous closure (1 second per 1 inch of size, roughly), there would be no reason not to be applied in safety standpoint, but it may not be as effective as that of continuous closure to avoid subsequent water hammer.
Posted 27 November 2024 - 11:28 PM
Is it allowable ESDV to have 2 step closure arrangement?
Yes, it is
Posted 29 November 2024 - 12:27 PM
Hi,
Find below the API RECOMMENDED PRACTICE 14C EIGHTH EDITION, FEBRUARY 2017. with expectation that could be helpful.
https://drive.google...iew?usp=sharing
Posted 30 November 2024 - 11:05 PM
thanks all...here two step for esdv is until 70 % of closure 1 inch /sec and balance 30% to 0% closure time is more than 1inch/sec ...is it acceptable such closure action in ESDV ..please clarify
regards,
stu
Posted 01 December 2024 - 11:08 PM
any closing pattern is acceptable depending on a hydraulic surge study
what does the hydraulic surge report say?
Valve Closure And Pressure Increase For Gas PipelineStarted by Guest_Root_* , 14 Aug 2021 |
|
|
||
Effective Valve Closure Time In Surge AnalysisStarted by Guest_SawsanAli311_* , 25 Apr 2020 |
|
|
||
Esdv Locations On A CompressorStarted by Guest_pklavins_* , 03 Jul 2014 |
|
|
||
Esdv & Sdv Opening And Closing Time [The Standard]Started by Guest_ikyikhram_* , 22 Jul 2013 |
|
|
||
By-Pass Line Around EsdvStarted by Guest_mm217_* , 01 Jan 2012 |
|
|